[Bldg-sim] ASHRAE 90.1-2007 G3.1.1.(b)
Bishop, Bill
bbishop at pathfinder-ea.com
Fri Dec 4 08:01:43 PST 2015
Chris,
I would use the ASHRAE 90.1 definitions for conditioned space and floor area, gross to make the determination, since Baseline systems are determined based on “conditioned floor area”. Your plenums and unconditioned spaces should most likely not be counted in conditioned floor area, since they are not conditioned, not counted as gross floor area (if less than 7.5’ headroom) or both. Spaces that aren’t part of your conditioned floor area shouldn’t factor into to the determination of thermal load intensity.
I generally only apply G3.1.1 Exception B. to spaces with high loads, such as the examples listed (server rooms etc.).
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image003.jpg at 01D12E83.278276B0] [cid:image005.jpg at 01D12E83.278276B0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Friday, December 04, 2015 10:25 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1-2007 G3.1.1.(b)
For determining the baseline system type, 90.1-2007 Appendix G, G3.1.1 list exceptions for determining the baseline system type. Exception (b) states that spaces with a peak thermal load that differs by 10 Btu/h*ft2 or more from the average of the other spaces served by the system are to be on a separate single zone system.
My question is about the word “served”. Are plenum and unconditioned zones on the system to be included in determining the average peak load? These spaces aren’t really “served” by the system.
I supposed plenums could be considered as served if the return air path is through the plenum?
Or do I assume all spaces on the system are “served” regardless of the space type (conditioned, unconditioned, plenum)?
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com<http://www.wspgroup.com/>
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151204/51c94c51/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 6574 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151204/51c94c51/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151204/51c94c51/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151204/51c94c51/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 3859 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151204/51c94c51/attachment-0007.png>
More information about the Bldg-sim
mailing list