[Bldg-sim] 90.1 - Exterior lighting parking
Julien.Dutel at mern.gouv.qc.ca
Julien.Dutel at mern.gouv.qc.ca
Thu Aug 6 13:57:59 PDT 2015
Hello,
In a project for a 24h retail, the exterior lighting need to comply to ASHRAE 90.1 2010 (zone 3). I'm focusing on table 9.4.3-B:
· In tradable surfaces, there is "Uncovered Parking areas/Parking areas and drive = 1.1 W/m2"
· In non-tradable surfaces, there is "Parking near 24-hour retail entrances = 800 W per Main entry"
My project has a main entry just next a 2000 m2 parking.
Does anyone know if I can add the 800 W to the 2200 W allowed for the parking (2000 m2 x 1.1 W/m2)?
Many thanks
Julien
Julien Dutel, ing., CEM, CMVP.
Direction des secteurs résidentiel, institutionnel et des affaires
Bureau de l'efficacité et de l'innovation énergétiques
Ministère des Ressources naturelles
5700, 4e Avenue Ouest, B-406
Québec (Québec) G1H 6R1
Téléphone : 418 627-6379, poste 8060
Téléphone sans frais : 1 877 727-6655
Télécopieur : 418 643-5828
http://www.efficaciteenergetique.mrn.gouv.qc.ca<http://www.efficaciteenergetique.mrn.gouv.qc.ca/>
AVIS DE CONFIDENTIALITÉ
Ce message est confidentiel. Il est à l'usage exclusif du destinataire ci-dessus. Si vous n'êtes pas le destinataire visé ou une personne autorisée à lui remettre cette communication, vous êtes par la présente avisé qu'il est expressément interdit de le diffuser, de le distribuer, de le reproduire, d'en dévoiler la teneur ou de prendre quelque mesure fondée sur l'information qui y est contenue. S'il vous a été envoyé par erreur, veuillez en informer immédiatement l'expéditeur par téléphone au 418 627-6379 et détruire ce message ainsi que toute copie de celui-ci.
P Devez-vous vraiment imprimer ce courriel? Si oui, pensez l'imprimer recto-verso!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150806/a82243c2/attachment.html>
More information about the Bldg-sim
mailing list