[Bldg-sim] 90.1 2010 - ERV - Fan Power Limitation Pressure Drop Adjustment
Julien.Dutel at mern.gouv.qc.ca
Julien.Dutel at mern.gouv.qc.ca
Wed Aug 26 09:06:58 PDT 2015
Bill,
Wow: my 3280 hp wouldn’t make sense at all…: I was mixed up between the SI and IP version and I forgot to divide by 4131 to find bhp.
So yes, you’re right: regarding only the ERV, adjustment would be 0,794 bhp, which need to be add to the rest of the VAV formula or the CV formula.
Thanks for you clear answer.
Julien Dutel, ing., CEM, CMVP.
Téléphone : 418 627-6379, poste 8060
De : Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Envoyé : 26 août 2015 11:46
À : Dutel, Julien (BEIE); Christopher.r.Jones at wspgroup.com; Duggin, Cory
Cc : bldg-sim at lists.onebuilding.org
Objet : RE: [Bldg-sim] 90.1 2010 - ERV - Fan Power Limitation Pressure Drop Adjustment
Julien,
You need to look at the rest of Table 6.5.3.1.1.A to do the calculation.
A = sum of (PD x CFMD/4131)
You do the calculation for each applicable device listed in Table 6.5.3.1.1.B. (As Cory mentioned, you only include the ERV adjustment if the baseline is required to have an ERV.)
For your ERV only, you have ((2.2 x 0.6) – 0.5) x (10,000 x 0.2)/4131 = 0.397 for each airstream, or 0.794 total.
With no other pressure drop adjustments, A = 0.794.
You then calculate total baseline fan power individually for each system, = CFMS x 0.00094 + A (for constant volume), using the baseline system supply CFM.
If, for example, the baseline system with energy recovery has 12,000 cfm supply airflow rate, bhp = (12,000 x 0.00094) + 0.794 = 12.074 bhp.
Then Pfan = bhp x 746 / Fan Motor Efficiency, using Table 10.8 for motor efficiency.
You have to split the value for Pfan between the supply, return, exhaust and relief fans in the baseline in the same proportion as the proposed design.
Hopefully I did that right and didn’t forget anything too important.
Best regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image001.jpg at 01D0DFF6.0735F570] [cid:image002.jpg at 01D0DFF6.0735F570]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[cid:image003.png at 01D0DFF6.0735F570]Carbon Fee and Dividend - simple, effective, and market-based.
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Duggin, Cory
Sent: Wednesday, August 26, 2015 11:20 AM
To: Julien.Dutel at mern.gouv.qc.ca<mailto:Julien.Dutel at mern.gouv.qc.ca>; Christopher.r.Jones at wspgroup.com<mailto:Christopher.r.Jones at wspgroup.com>
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] 90.1 2010 - ERV - Fan Power Limitation Pressure Drop Adjustment
It is worth noting that you only get to apply the baseline pressure drop adjustment for an ERV if the baseline is required to have an ERV.
Cory Duggin, PE, LEED AP BD+C
Associate/Energy Modeling Wizard, j.g.
[cid:image004.jpg at 01D0DFF6.0735F570]
TLC Engineering for Architecture
direct:
615-346-1939
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Julien.Dutel at mern.gouv.qc.ca<mailto:Julien.Dutel at mern.gouv.qc.ca>
Sent: Wednesday, August 26, 2015 10:04 AM
To: Christopher.r.Jones at wspgroup.com<mailto:Christopher.r.Jones at wspgroup.com>
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] 90.1 2010 - ERV - Fan Power Limitation Pressure Drop Adjustment
Here is a quick schematic of my project
[cid:image005.jpg at 01D0DFF6.0735F570]
During design condition (heating and cooling) economiser is off, wheel is on, and OA is at minimum (20% of the supply air). 10,000 cfm • 20% goes on each stream of the erv.
So based on your last answer the adjustment would be:
· Adjustement for supply air = 10,000 • 20% • ( (2.2 • 0.6 ) - 0.5 ) = 1 640 hp
· Adjustement for return air = 10,000 • 20% • ( (2.2 • 0.6 ) - 0.5 ) = 1 640 hp
Adjustments for the ERV would be : 1640 +1640 = 3280 hp
Am I correct ?
Thanks
Julien
Julien Dutel, ing., CEM, CMVP.
Téléphone : 418 627-6379, poste 8060
De : Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com]
Envoyé : 26 août 2015 09:48
À : Dutel, Julien (BEIE); bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Objet : RE: [Bldg-sim] 90.1 2010 - ERV - Fan Power Limitation Pressure Drop Adjustment
Hello Julien,
The entire formula is applied to each air stream, on the system, with an energy recovery device other than Runaround Coil.
When calculating A for each device, the flow CFMD, is the flow through the device, not the total system flow. For example, the flow through an enthalpy wheel might be the only the outdoor air portion of the total system flow.
It’s a good question though. I can see how the wording might trip you up.
[cid:image006.png at 01D0DFF6.0735F570]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065
www.wspgroup.com<http://www.wspgroup.com/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Julien.Dutel at mern.gouv.qc.ca<mailto:Julien.Dutel at mern.gouv.qc.ca>
Sent: Wednesday, August 26, 2015 9:32 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] 90.1 2010 - ERV - Fan Power Limitation Pressure Drop Adjustment
Hello,
With 90.1 2010, I wonder how to apply the fan power limitation pressure drop adjustment formula for an ERV:
(2.2 • Energy Recovery Effectiveness) - 0.5 in w.c. for each airstream
I don’t find example in the 90.1 user’s manual about ERV, does the “for each stream” statement apply to the “0.5 in w.c.” or to the all formula ?
With a 10,000 cfm ventilation fan and a sensible wheel with a 60% efficiency, what would be the pressure drop adjustment for the ERV?
• 10,000 • ( (2.2 • 0.6 ) - 0.5 • 2) = 3,200 hp
Or
• 10,000 • 2 • ( (2.2 • 0.6 ) - 0.5)=16,400 hp
It’s definitively not the same !
Thanks
Julien
Julien Dutel, ing., CEM, CMVP.
Direction des secteurs résidentiel, institutionnel et des affaires
Bureau de l'efficacité et de l'innovation énergétiques
Ministère des Ressources naturelles
5700, 4e Avenue Ouest, B-406
Québec (Québec) G1H 6R1
Téléphone : 418 627-6379, poste 8060
Téléphone sans frais : 1 877 727-6655
Télécopieur : 418 643-5828
http://www.efficaciteenergetique.mrn.gouv.qc.ca<http://www.efficaciteenergetique.mrn.gouv.qc.ca/>
AVIS DE CONFIDENTIALITÉ
Ce message est confidentiel. Il est à l'usage exclusif du destinataire ci-dessus. Si vous n'êtes pas le destinataire visé ou une personne autorisée à lui remettre cette communication, vous êtes par la présente avisé qu'il est expressément interdit de le diffuser, de le distribuer, de le reproduire, d'en dévoiler la teneur ou de prendre quelque mesure fondée sur l'information qui y est contenue. S’il vous a été envoyé par erreur, veuillez en informer immédiatement l'expéditeur par téléphone au 418 627-6379 et détruire ce message ainsi que toute copie de celui-ci.
P Devez-vous vraiment imprimer ce courriel? Si oui, pensez l’imprimer recto-verso!
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150826/916bc7a4/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150826/916bc7a4/attachment-0012.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150826/916bc7a4/attachment-0013.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3862 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150826/916bc7a4/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 6387 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150826/916bc7a4/attachment-0014.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 7941 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150826/916bc7a4/attachment-0015.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 6574 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150826/916bc7a4/attachment-0007.png>
More information about the Bldg-sim
mailing list