[Bldg-sim] Fan power calculations-MERV-16
Jim Dirkes
jim at buildingperformanceteam.com
Fri Apr 10 05:58:52 PDT 2015
Rathna,
Assuming the you are referring to an ASHRAE 90.1 Baseline, fan power is
unchanged except that you can claim a fan pressure credit. That is what
you appear to be referring to.
Each filter manufacturer will show pressure drop for a specific face
velocity. In the US, a typical face velocity is about 500 feet / min.
If the manufacturer filter pressure drop is .3" at 500 fpm (and the design
velocity is also 500 feet / min), then you can use 0.6" as your pressure
credit.
On Fri, Apr 10, 2015 at 8:33 AM, Rathna Shree <rathnashreep at yahoo.in> wrote:
> Dear All,
>
> We are working on a project with MERV 16 filters used in AHU. For the
> baseline case, pressure drop adjustment should be added and the description
> for the same is "calculate Pressure drop calculated at 2× clean filter
> pressure drop at fan system design condition". It would be very helpful if
> some one can explain what exactly that means and what has to be considered
> in base case fan power calculations.
>
> Regards,
> Rathnashree
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteamcom>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
The truth is still the truth, even if nobody believes it. A lie is still
a lie, even if *everyone* believes it.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150410/efe3a2c6/attachment-0001.html>
More information about the Bldg-sim
mailing list