[Bldg-sim] economiser for climate zone 1

Chris Yates chris.malcolm.yates at gmail.com
Thu Jun 13 04:04:50 PDT 2013


Hi Joe,

1a I understand. But we are looking at a 1b location (Hot/ Dry). Surely the
best approach would be economiser with DB control?

Curiously, in my copy (90.1 2007) economisers are not required in *1b
*(table G3.1.2.6A).
However, the following table (G3.1.2.6B) denotes that economiser high limit
shutoff should be 75degF for *1b*.

Am I missing something fundamental about the physics of non-extant
economisers?

Chris

On Thu, Jun 13, 2013 at 11:54 AM, Joe Huang <
yjhuang at whiteboxtechnologies.com> wrote:

> **
> I'm more agnostic about this. ASHRAE Climate Zone 1 (Miami) is very hot as
> well as humid.  Hopefully, there was some analysis done showing that
> economizers are not cost-effective under such climate regimes.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 108D
> Moraga CA 94556yjhuang at whiteboxtechnologies.comwww.whiteboxtechnologies.comhttp://weather.whiteboxtechnologies.com for simulation-ready weather data
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>
>
> On 6/13/2013 3:36 AM, Chris Yates wrote:
>
> Is it just me, or is does it seem terrifically wasteful that a climate 1
> building doesn't require an economiser? Or am I missing something?
>
>  KR / Chris
>
>
> _______________________________________________
> Bldg-sim mailing listhttp://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130613/c6654966/attachment.htm>


More information about the Bldg-sim mailing list