[Bldg-sim] LEED base design

Nick Caton ncaton at smithboucher.com
Tue May 22 08:10:39 PDT 2012


Hi there,


0.       I continue to generally advise against relying on the eQuest LEED compliance features at present.  This feature can be useful for one’s workflow, but only for the sum of modelers willing to carefully review the corresponding guidance that comes with eQuest 3.64.

1.       Strict reading of 90.1 language is the models should match.  If you’re getting at plenum zones however, it could be moot/appropriate for the models to differ in consideration of the system types and their respective return air path behavior.

2.       I haven’t yet) observed completely wrong constructions generated by the compliance feature myself, but can assert my past LEED reviewers have permitted some variance from what’s required/implied for baseline constructions in 90.1.  I feel two competent modelers can come up with different ‘correct’ interpretations for the same baseline construction.  That said, see point 0.  I would manually revise constructions for compliance.  If they really are way off, it could be productive to share your findings with members of the DOE2 development team (findable through the list archives).


Adding to point 0.:  Your “should I manually change…” query suggests you may not realize the compliance features of eQuest do not purport to do all work associated with a baseline model.  Review the associated guidelines carefully!  Help > Tutorials and Reference > LEED Analysis

[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Hussein Abaza
Sent: Tuesday, May 22, 2012 9:29 AM
To: bldg-sim
Cc: bldg-sim at onebuilding.org
Subject: Re: [Bldg-sim] LEED base design


Basic LEED questions. I am using the Compliance analysis in eQuest o generate the base design and my questions are
1- Does the base design has to have the same number of zones as the actual design ( the compliance analysis is generating less zones).
2- The compliance analysis generated R values much higher than what ASHRAE 90.1-2007 calls for. should I manually change them
Any help will be greatly appreciated
Thank you

________________________________
From: "Jason Glazer" <jglazer at gard.com<mailto:jglazer at gard.com>>
To: bldg-sim at onebuilding.org<mailto:bldg-sim at onebuilding.org>
Sent: Sunday, May 20, 2012 4:59:25 PM
Subject: [Bldg-sim] SPC209 Energy Simulation Aided Design Meeting in San        Antonio

ASHRAE SPC 209 Energy Simulation Aided Design for Buildings
Except Low-Rise Residential Buildings will be having our
first meeting during the upcoming San Antonio ASHRAE conference:

San Antonio
Tuesday June 26 8:00am - Noon
Convention Center at River Level Room 006B

For easy access to meetings in 006 follow signs to
convention center down escalator past the Hyatt restaurant
and enter the convention center, rooms are straight down the
hallway.

Jason
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120522/4221c85a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120522/4221c85a/attachment-0001.jpg>


More information about the Bldg-sim mailing list