[Bldg-sim] Virtual vs Scaled CEP modeling for LEED EAc1
韩星
foolishstar at 163.com
Fri Mar 2 21:12:50 PST 2012
I agree on this point if there is only one building of the hospital.
If there is more than one buildings in the hospital, I will choose option 1 I think.
At 2012-03-03 04:00:53,"Sami, Vikram" <Vikram.Sami at perkinswill.com> wrote:
I would follow #2
You need to figure out what the chiller sequencing is and factor that into your model too, but there is no reason why you shouldn’t model it as an on site chiller. When the lab comes online and if they seek to certify the lab, then I guess the lab would need to follow option1.
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com
Perkins+Will. Ideas + buildings that honor the broader goals of society
From:bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Madhav Munshi
Sent: Friday, March 02, 2012 2:51 PM
To:bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Virtual vs Scaled CEP modeling for LEED EAc1
Hi all,
We are modeling a new construction hospital whose cooling loads are met by 3 onsite 1350 ton chillers. A fourth ‘future’ 1350 ton chiller is added to this plant to provide supplementary cooling to an adjacent but future Lab building (the lab also borrows partial cooling from a campus CHW loop). All four chillers will be connected to the same primary chilled water loop, so essentially both the hospital and lab will feed off the same CHW loop. However, the hospital and Lab are being certified as two separate LEED NC projects.
For modeling the hospital only, should I
1. Create a virtual plant using Appendix C of the LEED DES guidelines and --model all upstream equipment, add a process load profile of the hospital and the lab to determine the average COP of the plant and then apply it to the hospital;
2. OR make an argument that we should be allowed to scale the plant as per the loads of the hospital since the plant is onsite. This will mean that, I will model the hospital as having only 3 onsite chillers and all related upstream equipment without following the LEED DES guidelines.
Any input will be appreciated.
Thank you
Madhav
Madhav Munshi, LEED AP BD+C
Environmental Designer
Atelier Ten
Environmental Design Consultants + Lighting Designers
45 East 20th Street, 4th Floor
New York NY 10003
T +1 (212) 254 4500 x212
F +1 (212) 254 1259
madhav.munshi at atelierten.com
www.atelierten.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120303/eccee849/attachment.htm>
More information about the Bldg-sim
mailing list