Thanks James.
But I'm afraid it is not that reason. I set the ground floor as adiabatic but the design air flow is still high, just very little lower compared to the previous one.
At 2012-02-26 20:42:21,"James Hansen" <JHANSEN at ghtltd.com> wrote:
It's almost surely your first floor slab. The default configuration and U-value for these constructions are usually very poor.
-James
On Feb 26, 2012, at 7:31 AM, "韩星" <foolishstar at 163.com> wrote:
Hi, every body,
I now have a difficult problem. I found that the autosized design air flow in the first floor is much larger than the second floor, about 5-10 times of the second floor. I cannot figure out the reason, because the indoor lighting, equipment power and the occupant density are all the same for the two floors.
In my opinion, the second floor should have a higher air-conditioning load than the first floor because it is the building's top floor. But the result is just the opposite.
I really want to know the reason and how I should deal with it.
Thanks
Xing
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120226/0e6f16b2/attachment.htm>
More information about the Bldg-sim
mailing list