Hi Ayzer,

You must make the system a Packaged VAV system.  The difference here is
that the cooling will come from a DX coil rather than a Chilled Water coil.

Hope this helps.

Rob

On Mon, Feb 13, 2012 at 12:14 PM, Ayzer Akguc <alpayakguc at yahoo.com> wrote:

> Hi,
>
> I would like to model a baseline building of Ashrae 90.1 2007
> conditioning with VAV system (system 5) in DesignBuilder. This system cools
> the building using DX cooling. However, I have branch errors when I model
> dx coils in vav system. Therefore, I would like to ask how I can model VAV
> system with DX cooling. If it is impossible using DesignBuilder, I would
> like to ask how I can model cooling system to be suited to system 5 in
> ASHRAE 90.1 Appendix G ?
>
> Best regards.
>
> Alpay Akguc
>
>