[Bldg-sim] Output Variable for Mass Flow Rate
Jim Dirkes
jim at buildingperformanceteam.com
Wed Feb 1 06:06:52 PST 2012
Dear Sachin,
Try these:
In the IDF:
Output:Variable, Name_dischargeNode, System Node Volume Flow Rate Standard
Density, Timestep;
In an RVI file:
Name_dischargeNode, System Node Volume Flow Rate Standard Density
In both cases "Name_dischargeNode" is the name that you are using for the
PTAC air outlet node.
The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653