[Bldg-sim] EE4: Boiler/Cooling Tower Set Points, and Max Heating COP

bfountain at greensim.com bfountain at greensim.com
Thu Apr 12 12:21:51 PDT 2012


2) Yup - 8 is as high as you can go.

1) The boiler setpoint (for a heat pump condenser loop) must be lower than the cooling tower setpoint which is set on the cooling tower tab.
Brian Fountain
bfountain at greensim.com

-----Original Message-----
From: Justin Elkin <jelkin at mreng.ca>
Sender: bldg-sim-bounces at lists.onebuilding.orgDate: Thu, 12 Apr 2012 16:00:14 
To: <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] EE4: Boiler/Cooling Tower Set Points, and Max Heating COP