[Bldg-sim] link between the change in air velocity to the equipment power consumption in Energy plus

Malherek, Elyse elyse.malherek at mcquay.com
Thu Sep 29 06:35:23 PDT 2011


Jawan,

Assuming you have the same air flow rates (but varying velocities), to change the energy consumption of the fan in EnergyPlus you will need to change the value of the Pressure Rise parameter in fan object (Fan:ConstantVolume or Fan:VariableVolume).  The increased velocity will change your pressure drop which will result in different energy consumption for varying velocities.

Elyse Malherek
Applications Engineer
McQuay International
a member of DAIKIN group
763.553.5379 (Office)
elyse.malherek at mcquay.com<mailto:elyse.malherek at mcquay.com>
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of JAWAN RAWAT
Sent: Thursday, September 29, 2011 4:26 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] link between the change in air velocity to the equipment power consumption in Energy plus


Dear all,

           Please suggest any link between the change in air velocity to the equipment power consumption in Energy Plus.