[Bldg-sim] Parking Structure - MNECB Lighting Power Density
Genest, Frederic
fgenest at pageaumorel.com
Mon Oct 31 13:47:04 PDT 2011
Greetings.
I assume that "standalone parking structure" refers to a multi-level building dedicated to car parking, and not an exterior parking lot.
Based on space functions, 10.8 W/m² seems to correspond to your description; I have the same understanding. However, noting that the building type method gives about 3 W/m² (depending on building area), I would suspect that there is a lot of other space types to account for.
MNECB does not appear to have any lighting prescriptions for exterior parking lot, if that is what you meant.
Hope this helps...
Regards,
Frédéric Genest,
Pageau Morel et associés inc.
ing., M.Sc.A., PA LEED BD+C / Eng., M.A.Sc., LEED AP BD+CASHRAE HBDP
Chargé de projet / Project Manager
Associé / Associate
fgenest at pageaumorel.com <mailto:fgenest at pageaumorel.com>
210, boul. Crémazie O., bur. 110
Montréal (Québec) H2P 1C6
T 514.382.5150 (203)
F 514.384.9872
www.pageaumorel.com <http://www.pageaumorel.com>
Poser un geste écolo : un engagement infini! Est-ce vraiment nécessaire d'imprimer ce courriel?
A green act: a commitment for infinity! Save trees. Print only when necessary.
AVERTISSEMENT CONCERNANT LA CONFIDENTIALITÉ / CONFIDENTIALITY MESSAGE
Ce courriel et toute information qui y est jointe sont confidentiels. Si vous avez reçu cette communication par erreur, veuillez nous en aviser immédiatement et effacer l'original, sans en tirer de copie ni en dévoiler le contenu. / This e-mail and any information enclosed are confidential. If you have received this message by error, please notify us immediately and delete the original without making a copy and without disclosing its content.
De : Brian Tysoe [mailto:BTysoe at mcw.com]
Envoyé : 31 octobre 2011 16:01
À : 'bldg-sim at lists.onebuilding.org'
Objet : [Bldg-sim] Parking Structure - MNECB Lighting Power Density
Hello,
Can anyone please confirm what MNECB Reference Building lighting power density should be assumed for a standalone parking structure?
My interpretation of Table 4.3.3.4 and Appendix E is that it should be 10.8W/m2, based on Space Function Storage Garage.
Thanks,
Brian Tysoe M.A.Sc., P.Eng., LEED AP
Mechanical Engineer
MCW Consultants Ltd. <http://www.mcw.com>
600-156 Front Street West
Toronto, ON M5J 2L6
Phone 416-598-2920
Fax 416-598-5394
This e-mail may be privileged and confidential. Any unauthorized use is strictly prohibited. If you received this e-mail in error, please contact the sender directly.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111031/b683fbc5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2843 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111031/b683fbc5/attachment.gif>
More information about the Bldg-sim
mailing list