[Bldg-sim] Baseline pump efficiencies
Bishop, Bill
wbishop at pathfinder-ea.com
Tue Oct 18 05:10:25 PDT 2011
Rathnashree,
1) The ASHRAE baseline pump power requirement has been discussed in
the equest-users forum. There was not a consensus, but the votes were
leaning toward splitting the 22W/gpm between the primary and secondary
pumps, and not assigning 22W/gpm to each pump. See the archives here:
http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010
-November/006942.html and here:
http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010
-December/007044.html
2) I believe the inputs for the chilled water pump power would be
"CCIRC-HEAD = 75", "CCIRC-IMPELLER-EFF = 0.65" and "CCIRC-MOTOR-EFF =
1.0".
3) Again, per the archive threads I provided, there was no
consensus. You need to make a judgment call on how to split the power
up.
4) I believe the inputs for CW pump power would be "TWR-PUMP-HEAD =
60.0", "TWR-IMPELLER-EFF = 0.60" and "TWR-MOTOR-EFF = 1.0".
Regards,
Bill
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rathna
Shree
Sent: Tuesday, October 18, 2011 1:54 AM
To: bldg
Subject: [Bldg-sim] Baseline pump efficiencies
Dear all,
ASHRAE 90.1 appendix G G.3.1.10 defines the base building pump power. I
have basic questions regarding this:
1) Is 22w/gpm for both primary and secondary pumps put together?
2) The user manual defines 22w/gpm as pump operating against a 75
foot head with 60% combined impellar and motor efficiency.
I work on Visual Doe. I have to input impellar efficiency and motor
efficiency separately. How do i input these values?
3) If 22w/gpm is including secondary pump, then what will be the head
and efficiencies for primary pump and secondary pump?
4) The condenser water pump power is 19 w/gpm. What is the head,
impellar efficiency and motor efficiency?
Looking forward for your replies.
Regards,
Rathnashree
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111018/a72db8ee/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111018/a72db8ee/attachment.jpeg>
More information about the Bldg-sim
mailing list