back in september there was a thread about what the outdoor air rate in a
baseline simulation should be compared to a proposed simulation,
specifically when one is adding 30% more outdoor air to meet the ieqc2
requirement and earn 1 leed point. there were differences of opinions
about the flow rates between baseline and proposed being either the same
(as required in 90.1 app g) or the baseline being the calculated per 62.1
and the proposed being as designed.
so i submitted a support request to the usgbc and the reply i received is
below, but in short the response is that unless you're using dcv
optionally the outdoor air rates in the baseline and proposed energy
simulations for eac1 should be the same. the response below gives the
standard responses to differing outdoor air rate scenarios.
regards,
patrick
[Fwd: Case 00531150: General LEED Questions
-------- Original Message --------
Subject:
Case 00531150: General LEED Questions [ ref:00D49UeD.5004GN692:ref ]
Date:
Mon, 17 Oct 2011 06:54:51 +0000 (GMT)
From:
"No reply GBCI" <mailto:no-reply at gbci.org> <no-reply at gbci.org>
<mailto:no-reply at gbci.org> <no-reply at gbci.org>
To:
patrick@
Dear Patrick,
Thank you for contacting the Green Building Certification Institute.
You ask very good questions related to the relationship between ASHRAE
Standards 62.1 and 90.1, and how these standards are applied across
multiple LEED Rating System prerequisites and credits.
The simple answer to your question is that, for systems without demand
controlled ventilation, the outdoor air included in EA Credit 1 energy
simulations must be the same in the Baseline and Proposed cases. If the
project is attempting IEQ Credit 2 Increased Ventilation, then the values
calculated in IEQc2 must be used in the EAc1 Basline and Proposed case
energy models. Note that IEQc2 does not limit the project to providing
only 30% more outdoor air than AHRAE 62.1 Ventilation Rate Procedure
minimums, so higher amounts are acceptable, as long as they are modeled
identically in both the Baseline and Proposed case energy models.
The following generic LEED Review Comment applies to ventilation systems
that do not have demand controlled ventilation:
It is unclear whether the minimum outside air rates (in CFM) were modeled
identically in the Baseline and Proposed case for all zones not having
Demand Control Ventilation in the Proposed case. Please confirm that
minimum outside airflow (in units of cfm) was modeled identically in the
Baseline and Proposed cases using the proposed case rates. Additionally,
please verify that all systems in both the baseline and proposed case are
modeled with zero outside air flow when fans are cycled on to meet
unoccupied setback temperatures unless health or safety regulations
mandate an alternate minimum flow during unoccupied periods (in which
case, the unoccupied outside air rates should be modeled identically in
the Baseline and Proposed case).
The situation becomes a bit more complicated in you have systems that have
demand controlled ventilation (often implemented as Carbon Dioxide control
of outdoor air or as programmed control of outdoor air based on occupancy
sensors.) In this case the Baseline case energy model must include the
minimum outdoor air as determined by the ASHRAE 62.1 Ventilation Rate
Procedure calculations for all systems having demand controlled
ventilation.
The following generic LEED Review Comment applies to ventilation systems
that do have demand controlled ventilation:
Demand control ventilation was modeled for credit in the proposed case.
Appendix G allows schedule changes for demand control ventilation as
approved by the rating authority (Table G3.1#4(Baseline)). As the LEED
Certification rating authority, GBCI requires that the outside air
ventilation rates for the Baseline case be modeled using minimum ASHRAE
62.1-2004 (or 2007 for LEED-NC 2009 projects) rates wherever credit is
taken for demand control ventilation in the Proposed case. The proposed
case minimum rates at design conditions should be modeled as designed.
Please verify that the Baseline Case model reflects ASHRAE 62.1-2004 (or
2007) minimum rates for any spaces where credit is taken for demand
control ventilation, or revise the model accordingly. For all other
spaces, please confirm that minimum outside airflow (in units of cfm) was
modeled identically in the Baseline and Proposed cases. Additionally,
please verify that all systems in both the baseline and proposed cases are
modeled with zero outside air flow when fans are cycled on to meet
unoccupied setback temperatures unless health or safety regulations
mandate an alternate minimum flow during unoccupied periods (in which
case, the unoccupied outside air rates should be modeled identically in
the Baseline and Proposed case).
Finally, even though you don't address energy recovery in your question,
whether or not you have energy recovery in your ventilation systems may
affect how much better (or worse) your Proposed case energy models perform
in relation to your Baseline case energy models.
The following generic LEED Review Comment addresses energy recovery in
EAc1 energy models as it relates to ventilation systems.
Energy recovery is modeled for credit in the Proposed case. Please provide
further information regarding the energy recovery efficiency, verify that
outside air is modeled with zero flow in both the Baseline and Proposed
cases during unoccupied periods when fans are cycled on to meet unoccupied
setback temperatures unless health or safety regulations mandate an
alternate minimum flow during unoccupied periods (in which case, the
unoccupied outside air rates should be modeled identically in the Baseline
and Proposed Case), and indicate the bypass mechanism used to bypass the
energy recovery during mild conditions.
I hope that helps, but if you have any further questions or concerns,
please feel free to use the contact form at http://www.gbci.org/contactus
and select "Follow up to GBCI Response," inputting your case number from
this email's subject line.
Best Regards,
Dan Katzenberger, P.E., CEM, BEMP, LEED-AP BD+C
Green Building Certification Institute
2101 L Street NW, Suite 500
Washington, DC 20037
800-795-1746 (phone)
202 828-5110 (fax)
www.gbci.org/contactus
The text above represents a staff opinion of a particular issue, and does
NOT set any precedent to be upheld during a LEED Certification Review. For
official rulings in advance of a LEED Certification Review, customers
should utilize the Formal Inquiries process available in LEED Online that
results in a Project Credit Interpretation Ruling (Project CIR) and
possibly a LEED Interpretation (formerly CIRs or Public Rulings).
Applications for LEED Certification will be thoroughly reviewed based on
USGBC Member balloted and approved LEED Rating Systems, with addenda, and
USGBC approved LEED Interpretations, or Project CIRs administered by GBCI,
as applicable. Please note that certain inquiries submitted to USGBC are
forwarded to GBCI for reply as appropriate.
_______________________________
CUSTOMER EMAIL ADDRESS:
patirck@
CUSTOMER INQUIRY:
I am trying to verify what the minimum outdoor airflow rate required for
EAc1 is and am not sure if this requires a CIR.
If the Proposed outdoor air ventilation is a minimum of 30% higher than
the minimum required by ASHRAE 62 in order to achieve 1 LEED point for
credit IEQC2 is the Baseline outdoor air rate also 30% higher than the
minimum required by ASHRAE 62? or would the Baseline outdoor air
ventilation rate be the minimum outdoor air rate per ASHRAE 62
calculations.
In other words, if ASHRAE 62 requires a minimum of 1,000 CFM of outdoor
air, and 1,300 CFM is provided to attain 1 LEED point via IEQC1, is the
Baseline outdoor air flow rate 1,000 CFM or 1,300 CFM in the energy
simulation?
90.1-2007/2004 both say the minimu m outdoor airflow rates shall be the
same for both the proposed and baseline building designs, as does the user
manual.
But this logic seems to reward the Proposed simulation by conditioning the
additional outdoor air supplied (300 cfm in the example above) to achieve
IEQC1 in the Baseline system as well as the proposed.
The logic of using the minimum required in the Baseline case is reflected
in EAC1 in the equipment efficiency requirements. Baseline efficiencies
are the minimum required, e.g. SEER 13 for packaged units.
It is the intent of the requirement that I am not sure is clear.
Increasing the outdoor air ventilation rate increases the energy used to
condition the outdoor air, so if the intent is to put the onus on Proposed
design to show energy reduction/LEED compliance over the 90.1/62
requirements shouldn't the Baseline outdoor air be the minimum air flow
rate per the ASHRAE 62 calculations? This puts the onus on the design team
to provide a design that compensates for the increase in energy to meet
IEQC2 by providing some method of processing the increase in outdoor air
while still reducing energy consumption.