[Bldg-sim] LEED Baseline system definition
Christopher Schaffner
chris at greenengineer.com
Wed Oct 12 17:31:53 PDT 2011
A basic principle of Appendix G is that fuel switching is not an energy
efficiency strategy, and shouldn't get rewarded. So the LEED interpretations
say that both baseline and proposed should use the same fuel with the same
rate structure, whether it is oil, gas, coal or biomass. However, depending
on the type and source of the biomass fuel, it may be considered "renewable"
for LEED. If it qualifies as a renewable energy source, the energy cost
becomes zero in the proposed case, and significant savings might be realized
under EAc1.
Check the LEED reference guide for the types of biomass that qualify as
renewable. Generally speaking it has to be agricultural waste, and must be
locally sourced.
--
Chris Schaffner, PE
LEED Fellow
Founder and Principal
The Green Engineer, LLP
Sustainable Design Consulting
50 Beharrell Street
Concord, MA 01742
T: 978.369.8978
M:978.844.1464
chris at greenengineer.com
www.greenengineer.com
The Green Engineer, LLP is a Certified B Corporation
From: Javier Duran <javier at b-green.cl>
Date: Wed, 12 Oct 2011 18:44:57 -0300
To: Nick Caton <ncaton at smithboucher.com>
Cc: <bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] LEED Baseline system definition
Hi everyone
During last week greenbuild at toronto i met a reviewer i and ask her what
kind of baseline system should i have when using biomass as heating fuel in
the proposed system.
She give me a different 'view': i should consider using biomass in both
buildings, so i could only take advantage of the energy efficiency of the
bioler (furnace) in the proposed, then i should consider the most used
system's efficiency in the zone.
what do you think?, still confusing for me!
--
Javier Durán Palma
Gerente General B-green SA
2011/9/1 Javier Duran <javier at b-green.cl>
> Hi Nick
> Thanks for the point, i think i will ask them before submitting, I´ll come
> back with the answer.
>
>
>
> --
> Javier Durán Palma
> Gerente General B-green SA
>
>
> 2011/9/1 Nick Caton <ncaton at smithboucher.com>
>> Hi Javier,
>>
>> I would arrive at the same conclusion based on a strict reading of 90.1.
>>
>> I can¹t speak directly for USGBC or its reviewership, but I would expect a
>> rational/logical individual who is permitted to review models in a
>> rational/logical fashion to at least consider accepting an alternate,
>> non-electric baseline system *if* you can make a strong case for why a
>> specific non-electric baseline would make for a fundamentally *better* system
>> upon which to found a performance rating. Perhaps circumstances specific to
>> the region of Chile you¹re working in mean an equivalent electric heating
>> source would be infeasible? I don¹t personally believe 90.1 & LEED are at
>> their core trying to make it inordinately easy *or* difficult for any
>> specific region or circumstance, but rather trying to make the procedure as
>> evenhanded as possible.
>>
>> Before taking any action (other than pursuing an ³electric or other² baseline
>> system), I would first suggest determining whether you can make such a case.
>> If so, take the actions necessary to pose your situation/query in a written
>> fashion to the correct parties through the proper LEED channels It¹s been
>> said your LEED project administrator may have an email for directing
>> project-specific questions to the appropriate parties outside of a formal
>> CIR.
>>
>> ~Nick
>>
>> NICK CATON, P.E.
>> SENIOR ENGINEER
>>
>> Smith & Boucher Engineers
>> 25501 west valley parkway, suite 200
>> olathe, ks 66061
>> direct 913.344.0036 <tel:913.344.0036>
>> fax 913.345.0617 <tel:913.345.0617>
>> www.smithboucher.com <http://www.smithboucher.com>
>>
>>
>> From: bldg-sim-bounces at lists.onebuilding.org
>> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Javier Duran
>> Sent: Wednesday, August 31, 2011 7:10 AM
>> To: bldg-sim at lists.onebuilding.org
>> Subject: [Bldg-sim] LEED Baseline system definition
>>
>>
>> Hi Everyone,
>>
>>
>>
>> We are working on LEED certification for a school project in the south of
>> Chile.
>>
>> The building has a wood pellet based biomass Boiler to provide heating. Since
>> the definition of the baseline system depends on the heating system of the
>> proposed building, I am wondering how to clasified the wood pellet boiler.
>>
>> The choices are:
>>
>> 1 fossil fuel,
>>
>> 2 electric or Other
>>
>> Should I consider wood pellet as " Other " and therefore the baseline system
>> would be Electric?
>>
>>
>>
>> Many Thanks,
>>
>>
>> --
>> Javier Durán Palma
>>
>> Gerente General B-green SA
>>
>>
>>
>
>
>
>
_______________________________________________ Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org To
unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111012/ba0e8da4/attachment.htm>
More information about the Bldg-sim
mailing list