[Bldg-sim] LEED Treatment of District Systems Pump Energy
Christian Kaltreider
ckaltreider at sudassociates.com
Wed Oct 12 05:47:15 PDT 2011
Thanks for this information, Bob. You are correct that I'm referring to the
earlier guideline (Required Treatment of District Thermal Energy in LEED
Version 2.2 and LEED for Schools, Version 1.0, 2008).
I should have been clearer in my post: This is a LEED 2.2 project, and the
model was originally created using the Version 1 guidance referenced above.
This project was started before the newer 2010 document (Version 2). The
model was submitted using the Step 1, Step 2 method of Version 1. I am now
trying to address the reviewer's comments. I did not create the original
model, but I have inherited it since the original modeler is not here any
longer. For addressing the comments, I think I should maintain the Version
1 format in which we submitted.
I'll do what seems to be most fair and accurate based on what I read in both
documents and the main intent of apples-to-apples comparisons. I was just
hoping someone else out there had come across this situation.
Thanks again,
Christian
From: Quitadamo, Bob [mailto:bquitadamo at RDKEngineers.com]
Sent: Tuesday, October 11, 2011 5:19 PM
To: Christian Kaltreider
Subject: RE: [Bldg-sim] LEED Treatment of District Systems Pump Energy
I think you may be referring to an outdated USGBC guideline.The most current
is here http://www.usgbc.org/ShowFile.aspx?DocumentID=7671 You should only
have to model option one OR option two, whichever you believe to be more
beneficial.
Bob Quitadamo | Mechanical Energy Engineer
RDK Engineers
Seaport Center, 70 Fargo Street, Suite 800, Boston, MA 02210
P: (857) 221-5927 | F: (617) 345-4226 | M: (978) 482-5629
bquitadamo at rdkengineers.com
http://www.rdkengineers.com <http://www.rdkengineers.com/>
cid:image001.png at 01CAF59E.2479A430
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Christian
Kaltreider
Sent: Tuesday, October 11, 2011 2:44 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED Treatment of District Systems Pump Energy
Hi Everyone,
I have not seen my specific situation adequately addressed in the LEED
documentation, so I would be interested to hear others' opinions on the
matter:
I am modeling a building which relies on a central plant for heating and
cooling. The plant serves only a few buildings. Heating enters the
buildings as HW, not steam. My building is designed such that there are no
hot water pumps.the BAS communicates back to the central plant pump system,
which adjusts flow appropriately. All flow within the building is
controlled by valves. My basic question is, in which models do I include HW
pump energy (that's 4 models.Step 1 Baseline and Proposed, and Step 2
Baseline and Proposed)?
Here are my thoughts. For certain I need to include HW pumps in the Step 2
Baseline, as for any Baseline using System 7. That leaves only 3 models to
ponder. The LEED guidance I have read leads me to believe I should include
HW pumps in Step 1 Baseline as well. The intention of Step 1 is to model
the buildings independent of the central plant, which would lead me to not
include the HW pump energy in my Step 1 Proposed model. Am I now cheating
by including the pump energy in the Baseline but not the Proposed for Step
1?
For Step 2, LEED documentation indicates that secondary pump energy needs to
be modeled in the proposed aggregate building/DES model. This would lead me
towards not modeling the central plant pumps, but again, is that cheating?
A portion of the central plant pump energy is certainly being used to push
water through my building.
Thanks for any thoughts/opinions you may have,
Christian
This e-mail message and any attachments are intended only for the designated
recipient(s). In addition, this message and its attachments, if any, may
contain information that is proprietary, confidential, or privileged and
exempt from disclosure or otherwise protected under applicable law. If you
are not the designated recipient of this message, you may not disclose,
reproduce, distribute, or otherwise use this transmission. Delivery of this
message to any person other than the intended recipient is not intended to
waive any right or privilege. If you have received this message in error,
please promptly notify the sender by reply e-mail and immediately delete
this message from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111012/9a5919e2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 15432 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111012/9a5919e2/attachment.png>
More information about the Bldg-sim
mailing list