[Bldg-sim] LEED and existing envelopes
James Hansen
JHANSEN at ghtltd.com
Tue Oct 11 11:30:34 PDT 2011
Thanks for the responses Anne and Bill. But this seems ridiculous, and
goes against everything I've done to date.
So if we have an existing building with no windows, and we want to reuse
the building structure/skin (which LEED strongly encourages), we get
penalized for wanting some daylight in the building?
I think all of the references to the "baseline building envelope shall
represent existing conditions" is intended to demonstrate that you can
use existing window and wall coefficients, NOT that you can't add
windows. But what do I know...
Does anyone know for sure?
GHT Limited
James Hansen, P.E., LEED AP
Senior Associate
1010 N. Glebe Road, Suite 200
Arlington, VA 22201-4749
703-243-1200 (office)
703-338-5754 (cell)
703-276-1376 (fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: Anne Juran [mailto:juran at summerconsultants.com]
Sent: Tuesday, October 11, 2011 2:02 PM
To: James Hansen; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] LEED and existing envelopes
I find existing envelopes always tricky because the information is not
delivered in the clearest manner. However, I think in this case the
reviewer is correct, based on 90.1 Table G3.1.5 item f under "Baseline
Building Performance" and page G-17 of the User's Manual. Also, in item
c they explicitly state that it applies to new buildings and additions,
but do not list existing (other than the little blip about alterations
and 5.1.3.)
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James
Hansen
Sent: Tuesday, October 11, 2011 10:23 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED and existing envelopes
I know this has been covered before, but I just received the following
comment from a GBCI reviewer for a v3 Core and Shell project I'm working
on. The project is basically an existing 5-story warehouse with almost
no windows. Part of the renovation is adding windows. The comment is
as follows:
Table 1.4.1B indicates that the window-to-gross-wall ratio is identical
in both cases; however it is unclear whether any fenestration was added
or removed as part of the renovation. The baseline ratio must reflect
the ratio as it existed prior to the renovation and the proposed ratio
must reflect the ratio as it exists after the renovation. Revise the
Baseline and/or Proposed cases as necessary so that the
window-to-gross-wall ratio is accurately modeled and provide a revised
prerequisite form and updated energy model output summaries as
necessary.
I didn't think that this was the case - I thought that if you had an
existing building, any EXISTING-TO-REMAIN windows would show up as the
existing window type, but any NEW windows in the proposed alteration
would be matched in the baseline model and comply with the Table 5.5
requirements. Meaning the WWR remained the 1:1 as long as it was < 40%
glass.
I think this is just a matter of educating the reviewer on our building,
but I wanted to make sure that there hadn't been a shift in how GBCI
reviews existing buildings.
Thanks!
GHT Limited
James Hansen, P.E., LEED AP
Senior Associate
1010 N. Glebe Road, Suite 200
Arlington, VA 22201-4749
703-243-1200 (office)
703-338-5754 (cell)
703-276-1376 (fax)
www.ghtltd.com <http://www.ghtltd.com/>
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111011/390bd8d1/attachment.htm>
More information about the Bldg-sim
mailing list