[Bldg-sim] ASHRAE 90.1 2007 Baseline System Selection
Cheney
chenyu73 at gmail.com
Mon Oct 3 16:59:24 PDT 2011
Hi Otto,
As per 90.1-2007 Addendum W, " Where attributes make a building eligible for
more than one *baseline *system type, use the predominant condition to
determine the system type for the entire building except as noted in
Exception a to Section G3.1.1." Since your lab < 20,000ft2, my understanding
is that you can use system 5.
Regards,
Cheney
LinkedIN @ http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b
On Mon, Oct 3, 2011 at 2:30 PM, Otto Schwieterman <oschwieterman at fhai.com>wrote:
> I am modeling a school that is 150,700 SF. There is a welding lab in the
> school and it falls within the exceptions of ASHRAE 90.1 2007: G3.1.1
> Exception b. (“Peak thermal loads that differ by 10 btuh/sf or more from the
> average of the other spaces served by the system…”). The welding lab is
> 3,500 SF and I would use System 3 (PSZ-AC) for this space.****
>
> ** **
>
> When I refer to Table G3.1.1A, one of the notes reads “Where attributes
> make a building eligible for more than one baseline system type, use the
> predominant condition to determine the system type for the entire building.”
> Does this allow me to use System 5 (Packaged VAV with Reheat) instead of
> System 7 (VAV with Reheat) since the predominant condition serves 147,200 SF
> (150,700-3,500)? ****
>
> ** **
>
> This is a LEED project and I would obviously rather use system 5 than
> system 7 as my baseline HVAC system.****
>
> ** **
>
> Thanks,****
>
> ** **
>
> Otto****
>
> ** **
>
> ** **
>
> ________________________________________________________________________________________
> Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
> designated individual or entity. If you received this message in error, please notify the sender by replying
> to the electronic mail (if electronic) or by telephone at the number indicated on this document.
> Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
> electronic mail. Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
> from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
> of this message by unintended recipients is not authorized and maybe unlawful. Any information included in
> this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
> Associates, Inc. may not be covered by our professional liability insurance.
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111003/65220e47/attachment.htm>
More information about the Bldg-sim
mailing list