[Bldg-sim] Parking Garage - Fan Operation Schedule

Bishop, Bill wbishop at pathfinder-ea.com
Fri Nov 18 08:19:53 PST 2011


Chris,

Check your local jurisdiction's mechanical code. For example, the 2010
Mechanical Code of New York State, Section 404, covers enclosed parking
garages. Systems, "shall be permitted to operate intermittently where
the system is arranged to operate automatically upon detection of
vehicle operation or the presence of occupants by approved automatic
detection devices." Otherwise, public garage exhaust has to operate
continuously per 502.13.

 

Regards,

Bill

 

  <mailto:wbishop at pathfinder-ea.com> 

 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Maria
Karpman
Sent: Friday, November 18, 2011 11:11 AM
To: 'Ioannis Rizos'; 'Chris'; 'bldg-sim at lists.onebuilding.org'
Subject: Re: [Bldg-sim] Parking Garage - Fan Operation Schedule

 

Garage exhaust runtime for different types of facilities and possible
savings from demand CO-ventilation controls depending on the type of
application are well covered in ASHRAE Applications Handbook Chapter 15.


 

Maria Karpman

LEED AP, BEMP

Karpman Consulting LLC

41C New London Turnpike 

Glastonbury, CT 06033

(860) 430-1909

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ioannis
Rizos
Sent: Friday, November 18, 2011 11:02 AM
To: Chris; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Parking Garage - Fan Operation Schedule

 

Hi Chris,

 

Try searching Appendix C - table 17 from the Green Star SA "ENERGY
CALCULATOR & MODELLING PROTOCOL GUIDE" for a start.

 

Hope that helps

 

Ioannis 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chris
Sent: 18 November 2011 15:58
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Parking Garage - Fan Operation Schedule

 

I'm looking for a documented schedule for the operation of
nonresidential buildings parking garage exhaust fans. 

 

Obviously we can use our engineering common sense and make a judgement
as to when, and for what duration, these fans might operate. What I'm
trying to find is a code or standard which documents this operation.

 

Thanks in advance for any help.

 

Chris


 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111118/7dfe57a7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 21646 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111118/7dfe57a7/attachment.png>


More information about the Bldg-sim mailing list