[Bldg-sim] usgbc response to outdoor air question

Martin Roy ing. LEED AP martin.roy at mra.qc.ca
Tue Nov 15 19:15:12 PST 2011


Ouch!
In the Model energy code in Canada only up to 20% 
more than ASHRAE 62 is allowed in the base 
case.  Imagine a building with 100% more OA and a 
ERV of 70% on the proposed case it can easily 
reach 10 EAcr1 point especially in cold climate.

Martin


At 21:41 15/11/2011, Reba Schaber wrote:
>Content-Language: en-US
>Content-Type: multipart/alternative;
> 
>boundary="_000_FAA9B7F58E5E4A46BDDF900F4CCAC3FE03ABA763DD3DPHSERVERphm_"
>
>RE:  “. . . can’t find) anything in 621.1 which 
>says that unoccupied ventilation should be zero.”
>
>I think this requirement comes from the mandatory provisions of 90.1.
>
>6.4.3.4.3 Shutoff Damper Controls. Both outdoor
>air supply and exhaust systems shall be equipped with motorized
>dampers that will automatically shut when the systems or
>spaces served are not in use. Ventilation outdoor air dampers
>shall be capable of automatically shutting off during preoccupancy
>building warm-up, cool down, and setback, except
>when ventilation reduces energy costs (e.g., night purge) or
>when ventilation must be supplied to meet code requirements.
>
>Thoughts??
>
>Reba
>
>From: bldg-sim-bounces at lists.onebuilding.org 
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jim Dirkes
>Sent: Monday, October 17, 2011 9:32 AM
>To: equest-users at lists.onebuilding.org; 'bldg-sim at lists.onebuilding.org'
>Subject: Re: [Bldg-sim] usgbc response to outdoor air question
>
>Dear Patrick,
>
>Thank you for sharing this GBCI response!  It is 
>very informative and, while I won’t admit that 
>I’ve been modeling anything incorrectly, I am 
>going to change a couple of things J.
>In particular, I have heard on several occasions 
>that the Increased Ventilation credit was a 
>clear case of “IEQ vs. energy”; you make a 
>decision to trade one against the other.  After 
>reading the GBCI response below and then 
>double-checking with ASHRAE 90.1, I find that 
>they are consistent with each other and 
>effectively allow no penalty for the increased 
>energy caused by increased ventilation.  Very 
>curious, considering there is no science which 
>demonstrates a health benefit for outdoor 
>airflows greater than that required by ASHRAE 62.1!
>The other item is that I failed to notice (and 
>still can’t find) anything in 621.1 which says 
>that unoccupied ventilation should be zero.  I 
>guess that is OK, but is also curious, since a 
>portion of the ventilation calcs in 62.1 include 
>consideration for off-gassing materials (which are always present.)
>All in all, I’m smarter than I was as a result 
>of your post, so it’s a good day!  Thanks again.
>
>The Building Performance Team
>James V. Dirkes II, P.E., BEMP , LEED AP
>1631 Acacia Drive NW
>Grand Rapids, MI 49504
>616 450 8653
>
>From: 
><mailto:bldg-sim-bounces at lists.onebuilding.org>bldg-sim-bounces at lists.onebuilding.org 
>[mailto:bldg-sim-bounces at lists.onebuilding.org] 
>On Behalf Of Patrick J. O'Leary, Jr.
>Sent: Monday, October 17, 2011 11:46 AM
>To: 
><mailto:equest-users at lists.onebuilding.org>equest-users at lists.onebuilding.org; 
><mailto:bldg-sim at lists.onebuilding.org>bldg-sim at lists.onebuilding.org
>Subject: [Bldg-sim] usgbc response to outdoor air question
>
>back in september there was a thread about what 
>the outdoor air rate in a baseline simulation 
>should be compared to a proposed simulation, 
>specifically when one is adding 30% more outdoor 
>air to meet the ieqc2 requirement and earn 1 
>leed point.  there were differences of opinions 
>about the flow rates between baseline and 
>proposed being either the same (as required in 
>90.1 app g) or the baseline being the calculated 
>per 62.1 and the proposed being as designed.
>
>so i submitted a support request to the usgbc 
>and the reply i received is below, but in short 
>the response is that unless you're using dcv 
>optionally the outdoor air rates in the baseline 
>and proposed energy simulations for eac1 should 
>be the same.  the response below gives the 
>standard responses to differing outdoor air rate scenarios.
>
>regards,
>patrick
>
>[Fwd: Case 00531150: General LEED Questions
>
>-------- Original Message --------
>Subject:
>
>Case 00531150: General LEED Questions [ ref:00D49UeD.5004GN692:ref ]
>Date:
>
>Mon, 17 Oct 2011 06:54:51 +0000 (GMT)
>From:
>
>"No reply GBCI" 
><mailto:no-reply at gbci.org><no-reply at gbci.org> 
><mailto:no-reply at gbci.org><no-reply at gbci.org>
>To:
>
>patrick@
>
>
>Dear Patrick,
>
>Thank you for contacting the Green Building Certification Institute.
>
>You ask very good questions related to the 
>relationship between ASHRAE Standards 62.1 and 
>90.1, and how these standards are applied across 
>multiple LEED Rating System prerequisites and credits.
>
>The simple answer to your question is that, for 
>systems without demand controlled ventilation, 
>the outdoor air included in EA Credit 1 energy 
>simulations must be the same in the Baseline and 
>Proposed cases. If the project is attempting IEQ 
>Credit 2 Increased Ventilation, then the values 
>calculated in IEQc2 must be used in the EAc1 
>Basline and Proposed case energy models. Note 
>that IEQc2 does not limit the project to 
>providing only 30% more outdoor air than AHRAE 
>62.1 Ventilation Rate Procedure minimums, so 
>higher amounts are acceptable, as long as they 
>are modeled identically in both the Baseline and Proposed case energy models.
>
>The following generic LEED Review Comment 
>applies to ventilation systems that do not have demand controlled ventilation:
>
>It is unclear whether the minimum outside air 
>rates (in CFM) were modeled identically in the 
>Baseline and Proposed case for all zones not 
>having Demand Control Ventilation in the 
>Proposed case. Please confirm that minimum 
>outside airflow (in units of cfm) was modeled 
>identically in the Baseline and Proposed cases 
>using the proposed case rates. Additionally, 
>please verify that all systems in both the 
>baseline and proposed case are modeled with zero 
>outside air flow when fans are cycled on to meet 
>unoccupied setback temperatures unless health or 
>safety regulations mandate an alternate minimum 
>flow during unoccupied periods (in which case, 
>the unoccupied outside air rates should be 
>modeled identically in the Baseline and Proposed case).
>
>The situation becomes a bit more complicated in 
>you have systems that have demand controlled 
>ventilation (often implemented as Carbon Dioxide 
>control of outdoor air or as programmed control 
>of outdoor air based on occupancy sensors.) In 
>this case the Baseline case energy model must 
>include the minimum outdoor air as determined by 
>the ASHRAE 62.1 Ventilation Rate Procedure 
>calculations for all systems having demand controlled ventilation.
>
>The following generic LEED Review Comment 
>applies to ventilation systems that do have demand controlled ventilation:
>
>Demand control ventilation was modeled for 
>credit in the proposed case. Appendix G allows 
>schedule changes for demand control ventilation 
>as approved by the rating authority (Table 
>G3.1#4(Baseline)). As the LEED Certification 
>rating authority, GBCI requires that the outside 
>air ventilation rates for the Baseline case be 
>modeled using minimum ASHRAE 62.1-2004 (or 2007 
>for LEED-NC 2009 projects) rates wherever credit 
>is taken for demand control ventilation in the 
>Proposed case. The proposed case minimum rates 
>at design conditions should be modeled as 
>designed. Please verify that the Baseline Case 
>model reflects ASHRAE 62.1-2004 (or 2007) 
>minimum rates for any spaces where credit is 
>taken for demand control ventilation, or revise 
>the model accordingly. For all other spaces, 
>please confirm that minimum outside airflow (in 
>units of cfm) was modeled identically in the 
>Baseline and Proposed cases. Additionally, 
>please verify that all systems in both the 
>baseline and proposed cases are modeled with 
>zero outside air flow when fans are cycled on to 
>meet unoccupied setback temperatures unless 
>health or safety regulations mandate an 
>alternate minimum flow during unoccupied periods 
>(in which case, the unoccupied outside air rates 
>should be modeled identically in the Baseline and Proposed case).
>
>Finally, even though you don't address energy 
>recovery in your question, whether or not you 
>have energy recovery in your ventilation systems 
>may affect how much better (or worse) your 
>Proposed case energy models perform in relation 
>to your Baseline case energy models.
>
>The following generic LEED Review Comment 
>addresses energy recovery in EAc1 energy models 
>as it relates to ventilation systems.
>
>Energy recovery is modeled for credit in the 
>Proposed case. Please provide further 
>information regarding the energy recovery 
>efficiency, verify that outside air is modeled 
>with zero flow in both the Baseline and Proposed 
>cases during unoccupied periods when fans are 
>cycled on to meet unoccupied setback 
>temperatures unless health or safety regulations 
>mandate an alternate minimum flow during 
>unoccupied periods (in which case, the 
>unoccupied outside air rates should be modeled 
>identically in the Baseline and Proposed Case), 
>and indicate the bypass mechanism used to bypass 
>the energy recovery during mild conditions.
>
>I hope that helps, but if you have any further 
>questions or concerns, please feel free to use 
>the contact form at 
><http://www.gbci.org/contactus>http://www.gbci.org/contactus 
>and select "Follow up to GBCI Response," 
>inputting your case number from this email's subject line.
>
>Best Regards,
>
>Dan Katzenberger, P.E., CEM, BEMP, LEED-AP BD+C
>
>Green Building Certification Institute
>2101 L Street NW, Suite 500
>Washington, DC 20037
>800-795-1746 (phone)
>202 828-5110 (fax)
><http://www.gbci.org/contactus>www.gbci.org/contactus
>
>The text above represents a staff opinion of a 
>particular issue, and does NOT set any precedent 
>to be upheld during a LEED Certification Review. 
>For official rulings in advance of a LEED 
>Certification Review, customers should utilize 
>the Formal Inquiries process available in LEED 
>Online that results in a Project Credit 
>Interpretation Ruling (Project CIR) and possibly 
>a LEED Interpretation (formerly CIRs or Public 
>Rulings). Applications for LEED Certification 
>will be thoroughly reviewed based on USGBC 
>Member balloted and approved LEED Rating 
>Systems, with addenda, and USGBC approved LEED 
>Interpretations, or Project CIRs administered by 
>GBCI, as applicable. Please note that certain 
>inquiries submitted to USGBC are forwarded to GBCI for reply as appropriate.
>
>
>_______________________________
>CUSTOMER EMAIL ADDRESS:
>patirck@
>
>CUSTOMER INQUIRY:
>I am trying to verify what the minimum outdoor 
>airflow rate required for EAc1 is and am not sure if this requires a CIR.
>
>If the Proposed outdoor air ventilation is a 
>minimum of 30% higher than the minimum required 
>by ASHRAE 62 in order to achieve 1 LEED point 
>for credit IEQC2 is the Baseline outdoor air 
>rate also 30% higher than the minimum required 
>by ASHRAE 62? or would the Baseline outdoor air 
>ventilation rate be the minimum outdoor air rate per ASHRAE 62 calculations.
>
>In other words, if ASHRAE 62 requires a minimum 
>of 1,000 CFM of outdoor air, and 1,300 CFM is 
>provided to attain 1 LEED point via IEQC1, is 
>the Baseline outdoor air flow rate 1,000 CFM or 
>1,300 CFM in the energy simulation?
>
>90.1-2007/2004 both say the minimu    m outdoor 
>airflow rates shall be the same for both the 
>proposed and baseline building designs, as does the user manual.
>
>But this logic seems to reward the Proposed 
>simulation by conditioning the additional 
>outdoor air supplied (300 cfm in the example 
>above) to achieve IEQC1 in the Baseline system as well as the proposed.
>
>The logic of using the minimum required in the 
>Baseline case is reflected in EAC1 in the 
>equipment efficiency requirements. Baseline 
>efficiencies are the minimum required, e.g. SEER 13 for packaged units.
>
>It is the intent of the requirement that I am 
>not sure is clear. Increasing the outdoor air 
>ventilation rate increases the energy used to 
>condition the outdoor air, so if the intent is 
>to put the onus on Proposed design to show 
>energy reduction/LEED compliance over the 
>90.1/62 requirements shouldn't the Baseline 
>outdoor air be the minimum air flow rate per the 
>ASHRAE 62 calculations? This puts the onus on 
>the design team to provide a design that 
>compensates for the increase in energy to meet 
>IEQC2 by providing some method of processing the 
>increase in outdoor air while still reducing energy consumption.
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send  a 
>blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG


----------

Martin Roy, ing. PA LEED®, président
Martin Roy et associés
1805 chemin Oka,
Deux-Montagnes, Qc
J7R 1N3


Tel: 450-623-0340
Cell. 514-594-6352

www.mra.qc.ca






Message de confidentialité
Ce courriel (de même que les fichiers joints) est 
strictement réservé à l'usage de la personne ou 
de l'entité à qui il est adressé et peut contenir 
de l'information privilégiée et confidentielle. 
Toute divulgation, distribution ou copie de ce 
courriel est strictement prohibée et peut être 
l’objet de poursuites judiciaires. Si vous avez 
reçu ce courriel par erreur, veuillez nous en 
aviser  et le supprimer de votre système 
informatique sans l'imprimer, le copier ou le faire suivre a quiconque.

Devez-vous vraiment imprimer ce courriel ?  Pensons environnement...
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111115/906dc539/attachment.htm>


More information about the Bldg-sim mailing list