[Bldg-sim] EE4 heating source
Marc-Antoine Paquin
marcantoine.paquin at mra.qc.ca
Mon May 30 10:52:41 PDT 2011
Hi Alex,
Define your system as a 2 pipes fan coil (or 4 pipe if you also do zone
cooling ). The heating at the zone level will be handled by the hot water
coming from your plant boiler. Define your plant boiler energy source as
electric. The energy consumption for your zone heating coil should then be
electric for the proposed and reference building.
You can also look in the EE4 modelling guide for 2 or 4 pipes systems
operation.
Dont hesitate if you have more questions.
Regards,
Marc-Antoine Paquin, eng.
cell. 514-402-9878
SignatureCouriel
Avis de confidentialité:
Les informations contenues dans ce message ou dans les documents ci-joints
sont de nature privilégiée et confidentielle. Elles ne peuvent être
utilisées quaux fins convenues par la personne ou lorganisme dont le nom
apparaît ci-dessus. Si la personne qui lit le présent message nest pas
celle à qui il est destiné, elle est priée de noter quil est strictement
interdit de divulguer, de distribuer ou de copier ce message. Si ce message
vous a été transmis par mégarde, veuillez le détruire et nous en aviser
immédiatement par courriel ou par téléphone.
De : bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] De la part de Alex Blue
Envoyé : 30 mai 2011 11:17
À : bldg-sim at lists.onebuilding.org
Objet : [Bldg-sim] EE4 heating source
I am using EE4 to model an office building with natural gas RTUs but
electric reheats at the zone level. The reference building is only using
natural gas for heating, rather than gas + electricity as in the proposed
design. Im getting very nice energy savings overall, but since my
electricity use for the proposed case is actually higher than that of the
reference, the cost has not gone down much at all (electricity is a lot
more expensive here than natural gas.)
Is there any way to get EE4 to model the electric zone reheat capacity in
its reference case?
I have the RTUs defined with electric zone reheat coils.
Thanks!
Alex Blue, EIT
P.S. Im new to the list, so hi! Nice to meet you all.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110530/2f4319d8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 23590 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110530/2f4319d8/attachment.jpeg>
More information about the Bldg-sim
mailing list