I guess that's the only possible route we can take. What possible options do we have if we cannot document a market standard equipment design? Their process is very unique and there are only a couple firms that do the process this firm does. 

 

I agree, even if we can get the baseline system variance to be approved, it will insignificant since the process load takes up the majority of the energy consumption.

 

William Mak, LEED AP BD+C
Mechanical Design Engineer

EPSTEIN
Architecture
Interiors
Engineering
Construction

600 West Fulton Street
Chicago, Illinois 60661-1259

D: (312) 429-8116
F: (312) 429-8800

E: wmak at epsteinglobal.com
W: www.epsteinglobal.com <http://www.epsteinglobal.com/> 

þ Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.

 

From: Cheney [mailto:chenyu73 at gmail.com] 
Sent: Tuesday, May 24, 2011 12:26 PM
To: Will Mak
Cc: Martin Roy ing. LEED AP; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Large Process Loads and Baseline Systems

 

Hi William, 

 

The "large process load" issue has been discussed extensively. Basically, the process loads are not allowed to be omitted from baseline and proposed design models. For your case, without touching the process loads, you probably have little chance to claim energy credit even you are allowed to modify the baseline. The possible solution will be the Process loads itself. See whether you are able to claim savings due to the introducition of high efficient equipments. Bear in mind, reduction of energy use in process loads is allowed as long as it is well documented with a comparison between market standard equipments (baseline) and energy-efficient ones (proposed design). By searching this forum or online, you will be able to find more info on this subject.  

 

Regards, 

 

Cheney

 

LinkedIN @ http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b <http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b>  





On Tue, May 24, 2011 at 9:14 AM, Will Mak <wmak at epsteinglobal.com> wrote:

Yes the project is a LEED 2009 project.

 

William Mak, LEED AP BD+C
Mechanical Design Engineer

EPSTEIN
Architecture
Interiors
Engineering
Construction

600 West Fulton Street
Chicago, Illinois 60661-1259

D: (312) 429-8116 <tel:%28312%29%20429-8116> 
F: (312) 429-8800 <tel:%28312%29%20429-8800> 

E: wmak at epsteinglobal.com
W: www.epsteinglobal.com <http://www.epsteinglobal.com/> 

þ Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.

 

From: Martin Roy ing. LEED AP [mailto:martin.roy at mra.qc.ca] 
Sent: Tuesday, May 24, 2011 10:57 AM
To: Will Mak
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Large Process Loads and Baseline Systems

 

Hi William, 
We did a Leed warehouse herre in Canada but it was version NC 1.0, your 2.2 version.
In that case process energy has to be remove for comparaison with baseline.
We aslo can reclaim up to 2 credit in process energy i.e. heat recovery from refrigeration.
If it is Leed 2009 than you have to include process energy in baseline and proposed.

Hope this help

Martin



At 11:38 24/05/2011, Will Mak wrote:

Content-class: urn:content-classes:message
Content-Type: multipart/alternative;
         boundary="----_=_NextPart_001_01CC1A28.AA99AA8A"

Hey all,
 
I'm about to begin a LEED energy model for a warehouse project that contains a very large process load. It will be a major renovation project. The building will be broken out as 50,000 sq ft office and 300,000 sq ft warehouse. The anticipated HVAC systems on the project are package rooftop units with DX cooling/gas heating for both the office and warehouse areas. The warehouse space requires cooling and heating.
 
Two issues that come to light:
 
1.       Large Process Load
a.       Anticipated process load will consume roughly 40-60% of the buildings annual energy consumption. The Exceptional calculation method has been considered. However, the process being done at this facility is extraordinary and there is not a "baseline" to compare savings off of.
2.       Baseline System
a.       Based on the size of the warehouse, System 7 will be modeled. This system is a packaged rooftop VAV with reheat with chilled water and hot water boiler system. Based on previous experience and preliminary modeling results, the baseline system will be more energy efficient than the package rooftop units with DX cooling/gas heating. There's been a suggestion by our team to request a LEED Interpretation and to possible change the baseline system to also packaged rooftop units with DX cooling/gas heating as that is typically designed for warehouse type facilities.
 
Based on these two issues, I am having a hard time foreseeing this project being able to hit the minimum 5% savings requirement on major renovations. I searched the LEED Interpretations database but didn't find one that dealt with a project that had both these issues.
 
Any suggestions? 
 
William Mak, LEED AP BD+C
Mechanical Design Engineer

EPSTEIN
Architecture
Interiors
Engineering
Construction

600 West Fulton Street
Chicago, Illinois 60661-1259

D: (312) 429-8116 <tel:%28312%29%20429-8116> 
F: (312) 429-8800 <tel:%28312%29%20429-8800> 
E: wmak at epsteinglobal.com
W: www.epsteinglobal.com <http://www.epsteinglobal.com/> 

þ Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.
 
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

________________________________


Martin Roy, ing. PA LEED®, président
Martin Roy et associés
1805 chemin Oka, 
Deux-Montagnes, Qc
J7R 1N3


Tel: 450-623-0340
Cell. 514-594-6352

www.mra.qc.ca






<http://www.mra.qc.ca/> Message de confidentialité 
Ce courriel (de même que les fichiers joints) est strictement réservé à l'usage de la personne ou de l'entité à qui il est adressé et peut contenir de l'information privilégiée et confidentielle. Toute divulgation, distribution ou copie de ce courriel est strictement prohibée et peut être l'objet de poursuites judiciaires. Si vous avez reçu ce courriel par erreur, veuillez nous en aviser  et le supprimer de votre système informatique sans l'imprimer, le copier ou le faire suivre a quiconque. 

Devez-vous vraiment imprimer ce courriel ?  Pensons environnement...


_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110524/db5c5886/attachment.htm>


More information about the Bldg-sim mailing list