[Bldg-sim] Energy Model Cost

Arpan Bakshi arpanbakshi at gmail.com
Fri May 13 06:09:17 PDT 2011


Marcus, thank you incorporating this language.

The one scenario we often see in our design guidance work is that a  
proposed design when compared with other design alternates does not  
necessarily provided the largest energy savings when compared against  
its own baseline case model. It is difficult to make a recommendation  
as consultants when we want to present the Owner with both real energy  
cost savings without compromising their LEED certification level  
targets.

A recent paper presented by the Weidt Group at SimBuild touched on  
this issue:

http://www.ibpsa.us/pub/simbuild2010/technicalPresentations/SB10-PPT-TS02A-03-Baker.pdf



Arpan Bakshi, LEED AP BD+C
YRG sustainability

On May 13, 2011, at 8:16 AM, "Marcus Sheffer" <sheffer at energyopportunities.com 
 > wrote:

> If anyone has any good ideas about how to structure the LEED credits  
> to end the practice of validation models at the end and encourage/ 
> require design phase modeling the folks on the USGBC EA TAG would  
> love to hear them.  The current proposed credit language from the  
> first public comment phase is listed below.
>
>
>
> NC, CS, SCHOOLS, RETAIL, WAREHOUSE & DISTRIBUTION CENTERS, HOSPITALITY
>
> Establish an energy performance target no later than the schematic  
> design phase. The target must be established as kBTU per square foot- 
> year of source energy use. This target must be mapped on the same  
> scale as the baseline and proposed buildings, if the project follows  
> Option 1.
>
>
>
> OPTION 1. Whole Building Energy Simulation
>
> Analyze a minimum of at least nine efficiency measures during the  
> design process and account for the results in design decision- 
> making. Analysis can include energy simulation of efficiency  
> opportunities, application of past energy simulation analyses for  
> similar projects to the project, or application of published data  
> from energy analyses performed for similar projects to the project  
> (such as AEDGs).
>
>
>
> A minimum of six energy efficiency measures focused on load  
> reduction strategies appropriate for the facility must be analyzed.  
> This analysis must be performed during the schematic design phase.
>
>
>
> A minimum of three energy efficiency measures focused on HVAC  
> related strategies must be analyzed (passive measures are  
> acceptable). This analysis must be performed before the conclusion  
> of the design development phase.
>
>
>
> The results of the analysis must be summarized in a brief report or  
> memorandum.
>
>
>
>
>
> The next version of LEED will be going out for public comment again  
> in July, I think, so please comment formally as well as discussing  
> here.
>
>
>
> Marcus Sheffer
>
> Energy Opportunities, Inc/a 7group Company
>
> 1200 E Camping Area Road, Wellsville, PA  17365
>
> 717-292-2636, sheffer at sevengroup.com
>
> www.sevengroup.com
>
>
>
> From: John Aulbach [mailto:jra_sac at yahoo.com]
> Sent: Thursday, May 12, 2011 7:46 PM
> To: Carol Gardner; Marcus Sheffer
> Cc: bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] Energy Model Cost
>
>
>
> OK, Carol..now you threw the "bait" out there..older than dirt, eh?
>
>
>
> I have done very limited LEED "type" modeling where you compare 20  
> walls and 40 windows types (well, it seemed that way). Correct me if  
> I am wrong, but a Base model must be built to comply with a certain  
> level of ASHRAE 90.1 (now up to 2010 ??). With all of the nuisances  
> of eQuest 3.64, I am going to build the model from scrathc and put  
> in all the relevant baseline data in by hand.  And, by the way, the  
> ASHRAE baseline model might be an entirely different system.  I am  
> just completing an EPACT evaluation (ASHRAE 90.1-2001) and the  
> Baseline HVAC was screwe chillers, whereas the Actual building was  
> packaged units with Turbocor compressors (ask me how I did that).
>
>
>
> It very much depends on the complexity of the building. A 40,000 sf  
> office or a 500,000 sf hotel with casino facilites.
>
>
>
> I am unfamiliar with the LEED paperwork to be filled out after the  
> modeling has been done. But I would not do anything of this type in  
> under 120 hours, preferably 160 hours. If the client thinks he can  
> do better, let him.
>
>
>
> Contingency, contingency.
>
>
>
> We won't discuss how old CAROL might be..
>
>
>
> John A.
>
>
>
> From: Carol Gardner <cmg750 at gmail.com>
> To: sheffer at energyopportunities.com
> Cc: bldg-sim at lists.onebuilding.org
> Sent: Thu, May 12, 2011 2:59:12 PM
> Subject: Re: [Bldg-sim] Energy Model Cost
>
> Marcus,
>
> You have inadvertently hit upon why IBPSA worked with ASHRAE to  
> create a BEMP certification. That's Building Energy Modeling  
> Professional (BEMP).
>
> Some of us who have been in the field for awhile began to worry a  
> couple of years ago when so many new energy modelers began appearing  
> on the listserv with questions. Their questions indicated a lack of  
> training and experience that was worrisome. What made it worrisome  
> was that they didn't seem to realize that they were as inexperienced  
> as they were; they didn't appear to be pursuing training to learn  
> how to do what they were doing; and we were uncertain as to how or  
> if they were practicing quality control. We hoped that by creating a  
> path to certification that we would give clients one more  
> qualification to look for in their modelers.
>
> If you have been in this industry for any length of time, and by  
> industry I mean the overall construction industry, you know that you  
> don't get a lot of chances if your work doesn't pan out. If your  
> energy model says I have a LEED Gold building and I'm going to save  
> $4,000/year and what I really get is LEED Silver and $1,000/year, I  
> am not going to be happy. So, I will probably not give you any more  
> work but, even worse for all of us, I'll start expressing doubts  
> about the whole process. LEED - what is it good for?
>
> So, now we all have more training, right? We read our ASHRAE  
> Handbooks and technical manuals so we know how to model the  
> difficult stuff. We can find any topic in the DOE2 Manuals, all of  
> which are one line, available, and easily searchable.
>
> So now we are so good we can do these models in 40-80 hours. Really?  
> Not me and I've been doing it longer than everyone, except you, John  
> Aulbach. So I'm going to join Marcus in his rant because he's on to  
> something.
>
> It's up to us to not under bid this work. It's up to us to educate  
> our clients about the importance of quality in this process. If they  
> think they are getting the same analysis in 40 hours that they used  
> to get in 120 hours, they need to be led around to rethinking that  
> and to be reminded that GIGO.
>
> Cheers,
>
> Carol
>
>
> Thu, May 12, 2011 at 2:31 PM, Marcus Sheffer <sheffer at energyopportunities.com 
> > wrote:
>
> In our experience a final model, done right, would take about 80  
> hours.
>
>
>
> WARNING – frustrated modeling rant to follow:
>
>
>
> Doing just a final model however completely misses the point as to  
> why we model – it is to guide design decisions!
>
>
>
> If I saw this RFP and all it asked me for was a model to determine  
> LEED points, during or after design, I would try to educate the  
> potential client about the purpose of modeling.
>
>
>
> Unfortunately too many projects pursuing LEED are only doing the  
> minimum when it comes to modeling and almost completely missing all  
> the benefits.  Too often the “market” transforms only based on a  
> least first cost denominator basis that results in little real trans 
> formation.  Doing models to determine LEED points does not transform 
>  the market, save any energy, and just circumvents the purpose behin 
> d LEED. (the next version actually requires design phase modeling!)
>
>
>
> Any “modeler” who does only final models without attempting to  
> explain to the owner why this is a bad idea should be “drummed out o 
> f the corp” in my humble opinion.
>
>
>
> The problem is that if you respond to this RFP with 120 or 160 or  
> more hours to really do the design phase modeling right, you will go  
> up against the “modeler” who claims to be able to do it in far  
> less time.  So how do we get the folks who issue the RFPs to ask for 
>  a proper scope of work so that they can compare fees on a level pla 
> ying field?  It is unfortunate that we are even having a discussion  
> about doing modeling work in opposition to its purpose.
>
>
>
> Sorry for the rant but I feel better now. J
>
>
>
> Marcus Sheffer
>
> Energy Opportunities, Inc/a 7group Company
>
> 1200 E Camping Area Road, Wellsville, PA  17365
>
> 717-292-2636, sheffer at sevengroup.com
>
> www.sevengroup.com
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim- 
> bounces at lists.onebuilding.org] On Behalf Of Demba Ndiaye
> Sent: Thursday, May 12, 2011 4:28 PM
> To: Omar Delgado; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] Energy Model Cost
>
>
>
> Omar,
>
>
>
> I would expect, for a building this size, approximately 40 hours  
> (multiply by your hourly rate). The 40 hours include EAp2/EAc1 LEED  
> documentation, and any review you may have to respond to later.
>
>
>
> Now, given that you have never done a LEED model, it will take you  
> more time, possibly up to 40 more hours.
>
>
>
> HTH,
>
>
>
> _______________
>
> Demba NDIAYE
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim- 
> bounces at lists.onebuilding.org] On Behalf Of Omar Delgado
> Sent: Thursday, May 12, 2011 7:08 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] Energy Model Cost
>
>
>
> Greetings everyone,
>
>
>
> I have a question regarding the cost of an energy model for a LEED  
> project. Every energy model I've done so far has been for
>
> existing buildings, mainly for optimization purposes. However, I  
> received an RFP to model a five-story, 41,500 sq. ft. building
>
> that's currently on the design phase and is pursuing the LEED-NC  
> Silver certification. I really have no idea what would be a fair
>
> price for this model since I'm going to have to use Appendix G  
> (ASHRAE 90.1) to evaluate the difference between the base
>
> and proposed buildings. I don't know how much extra effort this will  
> take. I know the procedure, just haven't done it before.
>
>
>
> Can you shed any light on this issue?
>
>
>
> Thanks in advance!
>
>
>
> Omar A. Delgado Colón, P.E., MEnvM., LEED AP BD&C
>
> Vice President
>
> EnerMech
>
> PMB 340
>
> 130 Winston Churchill Ave.
>
> San Juan, PR 00926-6018
>
> Cel. (787) 224-6537
>
> odelgado at enermechpr.com
>
> info at enermechpr.com
>
> www.enermechpr.com
>
>
>
>
>
>
>
> <image001.gif> Please consider your environmental responsibility  
> before printing this e-mail
>
> This Email is covered by the Electronics Communications Privacy Act,  
> 18 U.S.C. Sections 2510-2521 and is legally priviliged. The  
> information in this email is personal and confidential and is  
> intended solely for the addressee(s). Access to this email by anyone  
> else is unauthorized. If you are not an intended recipient, you must  
> not read, use or disseminate the information contained in the email.  
> Any views expressed in this message are those of the individual  
> sender and may be subject to Attorney/Client privilege and/or Work  
> Product. You are hereby notified that any dissemination,  
> distribution or copying of this communications is strictly prohibited.
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> -- 
> Carol Gardner PE
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110513/c609a307/attachment.htm>


More information about the Bldg-sim mailing list