[Bldg-sim] Simulating Curtain Wall in Energy Plus.

srishti srivastava ar.srishti at gmail.com
Thu May 12 00:51:03 PDT 2011


Thanks to all,

I would like to clarify the approach i have taken in the study at this
point of time.

The Building which is modelled is a sqaure block. There are five zones
(four aligned in the cardinal directions and one in the centre), the
depth of the zone is till 15 feet from the facade in each cardinal
direction.

Firstly, I am considering a glazed facade here,  which might be either
monolithic(one layer of glass) or Insulated Glazed Units (Double
layers of glass 6 mm thick with an air gap of 12 mm sandwitched
between them ). It is not a load bearing structure.There is no
insulation separately used in the facade.

Secondly, the glass is attached to the subframe which is subsequently
attached to the main frame(both of which are aluminium). Or it can be
directly attached to main frame.

In short, the facade which needs to be simulated is not an opaque
construction. Infact, it is fully glazed since i m considering a
window wall ratio as high as 90 percent also as one of the variables
in the study.

Thus, the question remains to be the same.
How to model curtain wall or rather curtain glazed facades in Eplus?
How will the modelling for such type of facade be different from
modelling a regular window?

I really appreciate the time spent and effort made by people reading
and replying to the thread.

Srishti.


On 5/11/11, Chris Yates <chris.malcolm.yates at gmail.com> wrote:
> Hi Pedro,
>
> Thanks for this - it's good to be up to date with the latest E+
> developments and this is a significant one.
>
> I'm not certain Srishti was asking about ventilated facades in the first
> instance. I just threw it in there in my first response and the thread
> has seemed to grow into a "ventilated facades" discussion!
>
> Best regards
>
> Chris
>
> On 10/05/2011 14:47, Pedro Peixeiro wrote:
>> Hello everyone.
>>
>> Chris,
>>
>> That limitation isn't present anymore. Solar radiation is partially
>> absorbed by the interzone ceilling and floor (and eventually walls if
>> present) but calculation is carried out to transmit the remaining
>> diffuse and direct radiation into the subsequent zone. Reflections are
>> also taken into account. But limitations still persist about shading
>> devices:
>> 1) they cannot be specificied to occupy just a fraction of the glazing
>> area (fully deployed or no shading at all);
>> 2) they can only be mounted on windows of exterior walls (though this
>> allows to model the shading device before, after and in between double
>> glazed windows of the exterior pane, it can't be be modeled for
>> shading devices on the inner pane, room side;
>> 3) there is still some limitations regarding airflow and convection
>> coefficient control between the shading device and the glazing itself,
>> because Eplus considers the shading device as a layer of the window it
>> is mounted on, and no direct control can be done for that in-between
>> window/shade air gap (this also prevents output results for the
>> interior window surface of the outside pane, only outside surface
>> temperature and shading temperature can be obtained).
>>
>> Srishti,
>>
>> So like it has been said, if you plan on simulating ventend facades in
>> which the inside pane is opaque, you can model them using the Exterior
>> Natural Vented Cavity object present in Eplus. If not, my advice is to
>> setup your facade as a vertical stack of two or more zones divided by
>> virtual partitions. Using Airflow Network objects, you can define all
>> the air dampers you need on the outside pane and also the ventilation
>> that occurs across the virtual partitions. Use Full Interior and
>> Exterior Solar Distribution with Reflections (remember to keep your
>> zone convex), choose a proper inside convection algorithm for the
>> cavity (I suggest ISO 15099 Windows), and you should come across some
>> relatively close results, considering the complexity of the problem
>> itself.
>>
>> Pedro.
>>
>>
>> On 10-05-2011 12:32, Francisco Massucci wrote:
>>> Srishti,
>>>
>>>   Here is the entire text. My ctrl+C, Ctrl+v failed last time, sorry.
>>>
>>> *SIMULATING DOUBLE SKIN FACADE*
>>>
>>> I'm simulating an office with a double skin façade using the
>>> "exterior vented natural cavity."
>>> The façade is naturally ventilated and has Venetian blinds in the
>>> gap. The blinds are exposed to solar
>>> radiation and, during the day, they can reach very high temperatures
>>> which may affect the temperature of the air in the gap and/or the
>>> performance of the glass façade. Does EnergyPlus take into
>>> account these two effects?
>>>
>>> *Answer*
>>> The exterior vented natural cavity model is for *opaque* surfaces
>>> only and does not apply to glazing
>>> systems. There is a model for blinds in the window gap that takes
>>> those two things into account, but I
>>> am not sure if it works together with the air flow window model.
>>>
>>> *Question*
>>> Thanks for your answer. I compared two simulations, one with the
>>> façade as exterior vented cavity
>>> and the other with the façade as a simple window, and it seemed that
>>> solar transmission through the
>>> glazing system is the same in both the cases. Even if the exterior
>>> vented cavity is only for opaque
>>> surfaces do you think it is possible to use the model for a glass
>>> façade, using as input the data of the
>>> glazing system  (thermal emissivity and solar absorbtivity)? Which
>>> differences or errors would occur
>>> using that model?
>>>
>>> *Answer *
>>> If I understand you correctly, I think what you are actually getting
>>> in the model is a regular window
>>> surrounded by a wall with a double skin. See if the inside face wall
>>> surface temperatures are different.
>>> The window shouldn't be changing.
>>> The exterior vented cavity model, which assumes that all the solar is
>>> blocked by a thin, solid layer on
>>> the outside, cannot be used for glazing. Opaque means no
>>> transmission. Inside EnergyPlus this
>>> becomes a special boundary condition for surface heat transfer
>>> modeling that is not available for
>>> window modeling. The window still gets exterior environment boundary
>>> conditions even though its
>>> parent surface has the exterior cavity boundary condition.
>>> Double façade improvements are being planned for the future.
>>>
>>> *Possible Workaround *
>>> if you really wanted to use the exterior vented cavity model on your
>>> DF, it could apply to a case where
>>> the double façade has totally opaque shades that are closed tight.
>>> You would use regular materials in
>>> the construction for the surface that approximate the DF (no
>>> subsurface and no glazing materials).
>>> The baffle in the exterior cavity model can get quite hot and then
>>> re-radiate infrared (but no
>>> shortwave) and convect to the underlying surface. But note that air
>>> gap models are much better
>>> developed for windows than for regular constructions; you would have
>>> to come up with thermal
>>> properties for each layer. One advantage of this approach might be a
>>> better model of transient
>>> behavior because the window models are always steady state.
>>> See also: EnergyPlus Technical Note – Opaque Ventilated Façades (July
>>> 2007 User News)
>>> On May 28, 2007, Emanuele Naboni (PhD Candidate), a visiting
>>> researcher from the Politecnico di
>>> Milano (Italy) gave a lecture at Lawrence Berkeley National
>>> Laboratory on how he used EnergyPlus to
>>> model Ventilated Opaque Façades.  A .pdf of his presentation is
>>> available at
>>> http://SimulationResearch.lbl.gov/reports.html under the heading "All
>>> EnergyPlus Reports."
>>> To save time, here is the direct link:
>>> http://simulationresearch.lbl.gov/dirpubs/vent_facade.pdf
>>>
>>>
>>> Francisco Massucci.
>>>
>>> On Tue, May 10, 2011 at 8:21 AM, Francisco Massucci
>>> <massucci at gmail.com <mailto:massucci at gmail.com>> wrote:
>>>
>>>     Srishti,
>>>
>>>       Try to found a topic named "Double Facades" on bldg-sim list. I
>>>     asked the same question some time ago.  The major problem in this
>>>     cases ,is the heat loss by convection inside de facade, because
>>>     otherwise it will percfectly work as a thin zone.
>>>
>>>      I found something on google, someone asking for an energyplus's
>>>     developer:
>>>
>>>     /I'm simulating an office with a double skin façade using the
>>>     "exterior vented natural cavity." /
>>>     /The façade is naturally ventilated and has Venetian blinds in
>>>     the gap. The blinds are exposed to solar /
>>>     /radiation and, during the day, they can reach very high
>>>     temperatures which may affect the temperature of the air in the
>>>     gap and/or the performance of the glass façade. Does EnergyPlus
>>>     take into /
>>>     /account these two effects? /
>>>     /Answer /
>>>     /The exterior vented natural cavity model is for *opaque*
>>>     surfaces only and does not apply to glazing /
>>>     /systems. There is a model for blinds in the window gap that
>>>     takes those two things into account, but I /
>>>     /am not sure if it works together with the air flow window model./
>>>     /
>>>     /
>>>     Please let me know if you do some progress. I'm from Brazil and
>>>     our climate conditions are very similar.
>>>
>>>     Good Luck,
>>>
>>>     Francisco Massucci
>>>
>>>     On Tue, May 10, 2011 at 5:10 AM, Chris Yates
>>>     <chris.malcolm.yates at gmail.com
>>>     <mailto:chris.malcolm.yates at gmail.com>> wrote:
>>>
>>>         Srishti,
>>>         I have no experience of the Therm/ LBNL Window link that you
>>>         speak of but as long as you're happy with working within the
>>>         limitations of the E+ shading calculation you should be fine.
>>>         I'm not sure of the latest E+ but the main historical
>>>         limitation I'm aware of is that solar gain to a zone is
>>>         absorbed by the floor (with some specific exceptions). This
>>>         is expedient for most simulation tasks but will not suffice
>>>         if you wish to model solar penetrating through subsequent
>>>         zones (within a double sheet facade, where the cavity is
>>>         modelled as a zone for example). The E+ documentation is
>>>         extensive and covers this in detail.
>>>         There are a number of options for the type of solar calc
>>>         undertaken. There are also options for convection
>>>         coefficient. You may find both of these affect results and
>>>         simulation time.
>>>         Good luck
>>>         Chris
>>>
>>>
>>>         On 10/05/2011 06:58, srishti srivastava wrote:
>>>>         Dear Friends,
>>>>
>>>>         I am Srishti Srivastava from India. My research topic is related
>>>> to
>>>>         evaluation of different types of facades in Indian context with
>>>>         special reference to the modern glazed facades.
>>>>
>>>>         I am trying to simulate a building with curtain wall in Energy
>>>> Plus. I
>>>>         know of one way of doing it through Window and Therm software
>>>> from
>>>>         LBNL, although there are few issues in that. Is there any
>>>> alternative
>>>>         way to simulate curtain wall in Energy Plus.
>>>>
>>>>         Does anyone have a prior experience of simulating curtain wall
>>>> in
>>>>         Energy Plus. Can anyone help me in simulating a curtain wall in
>>>> Energy
>>>>         Plus.
>>>>
>>>>         Thanks in advance.
>>>>
>>>>         Srishti Srivastava,
>>>>         India.
>>>>         _______________________________________________
>>>>         Bldg-sim mailing list
>>>>
>>>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>>>         To unsubscribe from this mailing list send  a blank message
>>>> toBLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>>> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>>>
>>>         --
>>>
>>>         Chris Yates C Eng MCIBSE
>>>
>>>         /Building Physics Consultant/
>>>
>>>         Tel:+447960731576
>>>
>>>         Email: chris.malcolm.yates at gmail.com
>>>         <mailto:chris.malcolm.yates at gmail.com>
>>>
>>>         Skype: christopher.m.yates
>>>
>>>
>>>         _______________________________________________
>>>         Bldg-sim mailing list
>>>
>>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>>         To unsubscribe from this mailing list send  a blank message
>>>         to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>>         <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> Bldg-sim mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>> To unsubscribe from this mailing list send  a blank message
>>> toBLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
> --
>
> Chris Yates C Eng MCIBSE
>
> /Building Physics Consultant/
>
> Tel:+447960731576
>
> Email: chris.malcolm.yates at gmail.com
>
> Skype: christopher.m.yates
>
>


More information about the Bldg-sim mailing list