[Bldg-sim] Appendix G - Fan power
Rosenberg, Michael I
michael.rosenberg at pnl.gov
Tue Mar 8 10:44:31 PST 2011
The 2010 version of Appendix G provides some good guidance.
G3.1.2.10.1 The calculated system fan power shall be
distributed to supply, return, exhaust, and relief fans in the
same proportion as the proposed design.
__________________________
Michael Rosenberg, CEM, LEED AP
Senior Research Scientist
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov<mailto:michael.rosenberg at pnl.gov>
www.pnl.gov<http://www.pnl.gov/>
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Hopf, Johannes
Sent: Tuesday, March 08, 2011 10:36 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G - Fan power
>From time to time we´re asked in LEED-Clarifications to break up the total fan-power into relief, exhaust, supply etc. Can somebody tell us what to do?
The calculation in the proposed is totally different and for the baseline we only use the 90.1 equations.
Johannes
Von: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] Im Auftrag von Sami, Vikram
Gesendet: Dienstag, 8. März 2011 17:11
An: bldg-sim at lists.onebuilding.org
Betreff: [Bldg-sim] Appendix G - Fan power
Does the dot in the equation indicate multiplication? So should the equation read CFMS X 0.0013 + A?
The reason I am confused is that they use X in other places.
[cid:image001.png at 01CBDD7D.CE5CA660]
Thanks in advance
We've moved! Please note our new address.
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com<mailto:vikram.sami at perkinswill.com> www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
Perkins+Will is carbon neutral. Learn more about our 2030 Challenge Estimating + Evaluation<http://2030e2.perkinswill.com/> tool for fossil fuel free buildings
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/acc0887b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 41690 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/acc0887b/attachment.png>
More information about the Bldg-sim
mailing list