[Bldg-sim] Fan Power

Corinne Benedek corinne.benedek at arup.com
Fri Jun 17 08:04:53 PDT 2011


Jason,

ASHRAE 90.1 2007 (and 2004) uses CFMs = "the baseline system maximum design supply fan airflow rate in cfm"

So it should be method 2. As Michael points out, you're not actually calculating the amount of power it takes  to supply 100,000 cfm.  You're calculating your "system allowance" based on that supply / total system airflow.  The calculations already are based on the idea that a supply of that quantity will have to return and/or exhaust that quantity as well.

The Advanced Energy Modeling for LEED manual also points out that  a common error is "Additional fan power allowance is claimed in baseline for return, exhaust, or relief fans".

-Corinne

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Michael A. Eustice
Sent: Friday, June 17, 2011 10:52 AM
To: 'Jason Wendel'; 'bldg-sim'
Subject: Re: [Bldg-sim] Fan Power

You seem to be directly correlating fan energy consumption and airflow rate.  Remember, fan energy is proportional to the product of airflow rate and differential pressure.

Here are my thoughts:

If we have:
SA fan: 100,000 cfm @ 4"wc
RA fan: 90,000 cfm @ 1" wc
EA fan: 10,000 cfm @ 1" wc

And let's say they result in:

SA fan: 95 KW
RA fan: 20 KW
EA fan: 2 KW

The total airflow of the system is 100,000 cfm, since the RA and EA fan are in series with the SA fan.  Remember, in a series arrangement the differential pressure of the fans are summed, not the airflow quantity; therefore, we meet the LEED criteria that says that the system total fan power is based on the baseline system design supply airflow rate.  The system total fan power, however, is 117 KW, which can be calculated by adding the individual fan's KW together, or by using total system airflow (100,000 cfm) and total system static pressure (5" wc) to calculate total system KW directly.  The system total differential pressure is 5", not 6", because the RA and EA fans are in parallel with each other, and both are in series with the SA fan.

Then I guess you'd simply apply that proportion of fan power (81% for SA fan, 17% for RA fan, and 2% for EA fan) to the proposed system configuration.

Can anyone else confirm?  I haven't done this calculation for LEED before so I am not saying this IS the correct approach.  This is simply my initial reaction to your question.

Thanks,
Michael Eustice, PE, LEED AP


From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jason Wendel
Sent: Friday, June 17, 2011 10:02 AM
To: 'bldg-sim'
Subject: [Bldg-sim] Fan Power

So, which is it, I have received LEED Review comments back stating two different ways to calculate fan power and no matter what I do, the next reviewer for the next project sees it differently and has me revise it.


1.       Calculate the baseline fan power from the sum of all the supply, return & exhaust airflows combined to get a total fan power.  Then proportion out the total fan power between each of the fans (supply, return, exhaust, etc).


2.       Calculate the baseline fan power for the supply fan only, and then proportion out the power from that calculation into each of the fans (supply, return, exhaust, etc.)

Method #1 takes all the airflow in all the fans in the building added together, calculates the fan power to move that much air, and then proportions it out to each of the fans.    For example, 100,000 cfm supply air, 90,000 return air and 10,000 exhaust air.  Totals to 200,000 cfm airflow in the building.  Calculate the airflow for the 200,000 cfm and lets say you get 200 kW.  Then you proportion out the fan power between the fans - but the sum is 200 kW of power.

So, method #2 doesn't make sense to me.  You take calculate the amount of power required to blow the supply air (lets say 100,000 cfm, for example) throughout the building (say 100 kW for simplicity), and then say that the 100 kW is then divided out between all the fans in the building, resulting in the supply fan using ½ of the power that you calculated it should, and the rest of the power is divided out between each of the other fans in the building.  So you calculate that 100 kW of energy is needed to move 100,000 cfm of air, but then you change your mind and say that the baseline system is actually only going to use 50 kW of energy and the other 50 kW is used in the return and exhaust fans?  That doesn't make sense to me.

So, which is it?  I've received review comments back from LEED stating each of them, for different projects.  It appears to be interpreted differently from different LEED Reviewers so apparently they don't know either.

-Jason


________________________________
The information contained in this message is intended only for the personal and confidential use of the recipient(s) named above. If the reader of this message is not the intended recipient or an agent responsible for delivering it to the intended recipient, you are hereby notified that you have received this document in error and that any review, dissemination, distribution, or copying of this message is strictly prohibited. If you have received this communication in error, please notify HT Lyons immediately, and delete the original message.
____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110617/28725ce4/attachment.htm>


More information about the Bldg-sim mailing list