[Bldg-sim] Balcony Heat Loss

Bishop, Bill wbishop at pathfinder-ea.com
Fri Jun 17 07:42:28 PDT 2011


Aaron,

 

Uninsulated assemblies are discussed in the User's Manual for ASHRAE
Standard 90.1. Page G-14 of 90.1-2010 User's Manual suggests:

"It is acceptable to model [projecting balconies] as having the depth of
the exterior wall they penetrate. For example, if the wall between the
intermediate floor slabs has a total depth of 8 in. (203mm), then these
assemblies can be modeled as being 8 in. (203 mm) thick. If the concrete
slab that forms the projecting balcony or intermediate floor slab for a
particular floor is 9 in. (229 mm) thick, then this section of the all
would be modeled in the proposed design as a 9 in. (229 mm) high
uninsulated concrete wall that is 8 in. (203 mm) thick."

 

Regards,

Bill

 

 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Brian
Fountain
Sent: Friday, June 17, 2011 10:39 AM
To: Aaron Smith
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Balcony Heat Loss

 

The accepted workaround is to add another wall type that is comprised of
12" of just concrete (U = 5.5 W/sq-m C) and has a height equal to your
slab thickness -- say 6".  So the area would be the wall length x the
slab thickness.

Not sure if this is clear -- it is better described on page 7-9 of the
EE4 modelling guide.

Brian

On 6/17/2011 10:20 AM, Aaron Smith wrote: 

Hello,

 

When performing energy modeling to determine compliance with the
Canadian Energy Code (MNECB), penetrations through the building envelope
must be taken into account when calculating wall R-values if their area
exceeds 2% of envelope area.  I'm working on a LEED project and trying
to calculate the wall R-value of a Hotel taking into account heat losses
from the balconies which are extensions of the floor slab (balcony
penetrations exceed 2% of envelope area).

 

I realize this is a rather complex heat transfer problem but hope there
may be an easy approximation.  My first thought was to treat them like a
parallel path heat transfer problem: 1/Req = %slab/Rslab + %wall/Rwall
but I'm thinking that may not be fair (perhaps this would be used if you
had concrete studs in the wall).  My other thought is to treat the slab
penetrations as a separate wall type (uninsulated concrete wall) - this
would have a reduced affect on the overall wall R-value.  

 

Does anyone have thoughts on this?

 

Thanks,

Aaron

 

Aaron Smith, P.Eng 

LEED(r) AP BD+C, M-ASHRAE, Mechanical Engineer

 

t: (902) 422-7393

f: (902) 423-4945

e: asmith at mreng.ca <mailto:asmith at mreng.ca> 

 

The electronic message contained herein is private and confidential,
intended only for the recipient(s) specified. If you have received this
message in error, please delete it and notify us immediately.  Any
accompanying files are supplied as a matter of courtesy only.  The data
are without warranty of any kind.  Any person or business making use of
the data is responsible for confirming its accuracy and completeness.
M&R Engineering Ltd. is not responsible for edited or produced versions
of this digital information. 

 

 
 
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG






No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1382 / Virus Database: 1513/3709 - Release Date: 06/17/11

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110617/825c812c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20862 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110617/825c812c/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1860 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110617/825c812c/attachment-0001.jpeg>


More information about the Bldg-sim mailing list