[Bldg-sim] ventilation schedules for PTAC vs central outside air AHUs?

Robby Oylear robbyoylear at gmail.com
Thu Jul 21 10:04:49 PDT 2011


As long as you're delivering the same quantity of outside air in both models
on an hourly basis, and accounting for how the proposed system will actually
operate, I'd say yes.  If for any reason your ventilation air operates
intermittently in the proposed design, you would need to schedule it the
same way in the baseline.

*Robby Oylear, LEED**®** AP BD+C*

*Mechanical Project Engineer*

*Energy Analyst*

* *

*D* 206-788-4571 | *C* 206-354-2721

*www.rushingco.com* <http://www.rushingco.com/>

On Thu, Jul 21, 2011 at 9:20 AM, James Hansen <JHANSEN at ghtltd.com> wrote:

> I was curious if anyone knew whether the following is allowed in accordance
> with Appendix G (and/or LEED):****
>
> ** **
>
> If have a hotel where the baseline system is PTAC, and those units are
> intended to be the source of ventilation air, I have to have the fans run
> continuously per Appendix G.****
>
> ** **
>
> If my proposed building has a central OA delivery system that introduces OA
> directly to each room, can I have that system run continuously and allow my
> FCUs in each hotel room to run intermittently?****
>
> ** **
>
> Thanks for any advice!****
>
> ** **
>
> *GHT Limited
> **James Hansen, P.E., LEED AP*
> Senior Associate
> 1010 N. Glebe Road, Suite 200
> Arlington, VA  22201-4749
> 703-243-1200 (office)****
>
> 703-338-5754 (cell)
> 703-276-1376 (fax)****
>
> www.ghtltd.com****
>
> ** **
>
> ------------------------------
> The information contained in this communication is confidential, may be
> privileged, and is intended only for the use of the addressee.  It is the
> property of GHT Limited.  Unauthorized use, disclosure or copying of this
> communication or any part thereof is strictly prohibited and may be
> unlawful.  If you have received this communication in error, please notify
> me immediately by return e-mail or by e-mail to ght at ghtltd.com, and
> destroy this communication and all copies thereof, including all
> attachments.  Thank you.
>
>  <#1314d827e3eacd38_>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110721/8c4f1cc4/attachment.htm>


More information about the Bldg-sim mailing list