Nick,

I would do it with schedules.  This would be the long method.

I have the same controls and have not got around to model it.  I would also
make many schedules.  A different schedule for occupancy, lights, equipment,
ect.  Also if this applies to a lot of rooms, you'd likely make multiple
schedules, one assuming that the room is empty from 9~10 another room empty
from 2~3.  (The inverse for meeting rooms, if you have multiple meeting
rooms, not all meetings will happen at the same time.)


"Is Freedom a small price to pay to stop Global Warming?"

John Eurek PE, LEED AP
Mechanical Engineer,

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Tuesday, July 19, 2011 3:59 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] How have you approached...

I have a precedent question for everyone... this is not a "how to" procedural
question for any particular software, but to simply feel out what has worked
for others in the past:

 

Here's a quick description of the situation at-hand:  a VAV terminal unit
with a "normal" minimum damper position (say, 30%) is tied by relay to the
space occupancy sensor, which also controls the lights.  Upon sensing space
vacancy, the minimum airflow damper position is reset to 0% (airflow is
permitted to stop, provided thermostat temperature set point is satisfied).
Upon sensing occupancy, the preset minimum damper position is restored.

 

For LEED/USGBC-reviewed energy models, can anyone relate success in modeling
this or a similar energy-saving behavior in the proposed model, distinct from
the baseline?  If so, what approach did you use to model this behavior and/or
quantify the energy savings? 

 

I was discussing the possibilities with some colleagues and have a few ideas
for approaches that might all be justifiable, ranging from simple (and quick)
to complex (and time-consuming).  

 

There are likely multiple "right" answers here, but I am hoping to identify
some precedent to understand what we can anticipate the LEED reviewership
will accept.  

 

Thanks in advance!

 

~Nick

 

cid:489575314 at 22072009-0ABB

 