[Bldg-sim] Fwd: insulation film on windows in EnergyPlus
Marcus
jones.0bj3 at gmail.com
Tue Jul 12 02:06:12 PDT 2011
I don't think a WindowMaterial:Shade will properly account for the film, I
would instead look into creating your window in the software WINDOW from
LBL. This software can model detailed layer-by-layer windows with frames and
full spectral data, which can then be exported into EnergyPlus.
http://windows.lbl.gov/software/window/window.html
Good luck and I hope you let us know your solution!
P.S. EnergyPlus talks about the SHGC or g-Value of windows, not shading
coefficients. You can convert between them.
Marcus
--
Marcus Jones, LEED AP, M.Sc.
*Freelance energy consultant*
*Vienna, Austria*
2011/7/11 윤정훈 <superfig at hotmail.com>
> Hello,
>
> I'm running simulation wih EnergyPlus.
> In order to apply ECMs, I'm trying to apply insulation films to each
> window.
> The object I used is *WindowMaterial:Shade*, but I don't think my way is
> correct.
> I have limited information (Available data include solar reflectance,
> visible reflectance/transmittance, and shading coefficient),
> which is further complicating the situation.
>
> Any help will be much appreciated.
> Thank you.
>
>
> _Jeong
>
> p.s. BTW, I do not understand why there's no shading coefficient field in
> window-related objects.
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Marcus Jones, LEED AP, M.Sc.
*Freelance energy consultant*
*Vienna, Austria*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110712/447ff9d6/attachment.htm>
More information about the Bldg-sim
mailing list