[Bldg-sim] Do Energy Codes apply to replacing HVAC equipment?
Varkie C Thomas
thomasv at iit.edu
Fri Jan 28 14:24:58 PST 2011
Thanks for all the replies. I should have done my homework before asking the question. ASHRAE Std90 is clear on this topic but with the Minnesota Energy Code you have interpret �remodeled elements� to include everything besides the structure
Minnesota Energy Code Chapter 7676 � All Buildings except low-rise residential
Application:
2. New & remodeled elements of buildings. This Chapter applies to all new and remodeled elements of commercial and all other buildings.
3. Existing Buildings. Additions, alterations and repairs to existing buildings or structures must comply with part 7676.1400.
ASHRAE Std90-2004
4.1.1.5 Changes in Space Conditioning. Whenever unconditioned and semi-heated spaces are converted to conditioned spaces, such conditioned spaces shall be brought into compliance with all the applicable requirements of this standard that would apply to the building envelope, heating, ventilating, air-conditioning, service water heating, power, lighting, and other systems and equipment of the space as if the building were new.
I would like to have your views and opinions on Articles 1 and 2 (open website http://bepan.info click on tab Articles at the top and then the articles to open the file.
Article-1 Architectural Design and the Perimeter Zone.
Article-2 Mechanical Design and Percent Energy Savings
The website contains the teaching notes and examples of building energy use that I used for graduate courses and advising doctoral candidates. I put them on a website, before throwing it all away, in case it might useful to others. The objectives are in the Introduction.
Varkie
----- Original Message -----
From: Nick Caton <ncaton at smithboucher.com>
Date: Friday, January 28, 2011 2:41 pm
Subject: RE: [Bldg-sim] Do Energy Codes apply to replacing HVAC equipment?
> Hi Dr. Varkie!
>
>
>
> Your question hinges directly on which energy code/standard is being
> enforced.
>
>
>
> While someone on these lists might know definitively... this is a
> question that is probably best answered by the local planning
> departmentthat issues permits. I would advise calling, ask what
> energystandard/code (if any) is adopted and whether review of that
> code/standard is part of the permit review process (energy codes
> in some
> areas are adopted, but not enforced). You may be able to speak
> directlyto the person who performs these reviews and if so she/he
> may be able to
> give you a direct answer to your specific question of scope.
>
>
>
> ~Nick
>
>
>
>
>
>
>
> NICK CATON, E.I.T.
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of David
> Eldridge
> Sent: Friday, January 28, 2011 1:19 PM
> To: Varkie C Thomas; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] Do Energy Codes apply to replacing HVAC
> equipment?
>
>
>
> Varkie, not sure if you got any replies to this one. 6.1.1.3 in
> 90.1-2007 says that direct replacement equipment should still meet the
> mandatory efficiencies.
>
>
>
> David
>
>
>
>
>
>
> David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, HBDP
>
> Grumman/Butkus Associates
>
>
>
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
> Varkie C
> Thomas
> Sent: Wednesday, January 26, 2011 1:20 PM
> To: 'bldg-sim at lists.onebuilding.org'
> Subject: [Bldg-sim] Do Energy Codes apply to replacing HVAC equipment?
>
>
>
> Does a condo bldg (400,000 sf, 28 flrs, built 1985, Minneapolis)
> have to
> comply with the energy code when replacing the plant equipment?
>
> Varkie Thomas
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110128/7f193f32/attachment.htm>
More information about the Bldg-sim
mailing list