[Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1
Ashraf Khan
ashraf at mecsd.com
Wed Jan 26 05:14:54 PST 2011
Hello James,
I accept that ASHRAE 62.1 is concerned with people, the same we explained to
LEED Reviewer team, this is the comment we received,
However, since the project uses ventilator fans it is considered a
mechanically ventilated space. Additionally, the LEED-NC v2.2 IEQp1 CIR
ruling dated 10/8/2008 states that unless the mechanically ventilated
warehouse has no human occupancy except for maintenance and repairs it must
meet the requirements of ASHRAE Standard 62.1-2004. The narrative states
that the warehouse will be occupied for the loading and unloading of goods;
therefore, the warehouse is regularly occupied.
Provide calculations for the warehouse space demonstrating that the space
complies with the minimum requirements of ASHRAE Standard 62.1-2004.
I am not having any idea how to convince the team.
Thanks & Regards,
Ashraf
_____
From: James V Dirkes II, PE [mailto:jvd2pe at tds.net]
Sent: Wednesday, January 26, 2011 3:46 PM
To: 'Ashraf Khan'; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1
Ashraf,
ASHRAE 62.1 is concerned with people, who need ventilation (supply /
intake). For typical buildings, you may not need separate exhaust fans,
because that amount can probably exfiltrate through cracks. Supply and
exhaust fans can be used in tandem if the building is fairly tight (no
leaks).
Your MEP team's 5-8 air changes per hour is for cooling, not ventilation.
Any building with which has that much infiltration is closer to a tent than
a building! (It's not closed up.)
The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ashraf Khan
Sent: Tuesday, January 25, 2011 11:55 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1
We received a LEED review comment regarding Warehouse ventilation to comply
with ASHRAE 62.1-2004.
Generally depending on the warehouse storage, MEP team recommends 5-8 Air
Changes per Hour by thumb rule for exhaust and air intake is assumed by
infiltration by windows, open doors etc.. But this number I haven't find in
ASHRAE, please give me reference.
ASHRAE 62.1-2004, Table 6-1 for warehouse category says to have 0.06
cfm/ft2, is this number defines to intake or Exhaust? If it is exhaust, it
is too small as volume of warehouse will be high.
Please share your ideas to comply with the requirements.
Thanks & Regards,
Ashraf
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110126/c653dc36/attachment.htm>
More information about the Bldg-sim
mailing list