[Bldg-sim] Unmet hours

Kris Raj kris_raj at rocketmail.com
Fri Jan 14 09:34:01 PST 2011


Hello,
            I am investigating the reason why a zone has a high number of hours 
with heating load unmet. I printed out the hourly report variables from the 
thermal zone [attached]. This zone has a very low internal load hence when the 
thermostat is returned to normal from the setback it does not gain a lot of 
heat. I see that the system is able to supply at the design supply temperature 
of 90 F. However the CFM does not increase beyond the 40% minimum flow ratio. It 
appears that the system is supplying enough energy to meet the instantaneous 
load. However it is not looking to meet the lack of heat due to the heat 
capacity.
 
Could anyone please explain why the program is not calculating a higher supply 
air flow rate that would be required to meet the set point temperature.
 
Thanks,
Kris


      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110114/919861c6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Hourly Report.GIF
Type: image/gif
Size: 93808 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110114/919861c6/attachment.gif>


More information about the Bldg-sim mailing list