So the interpretation would be that we must model the baseboard system with
whatever HVAC system is associated with the design while the baseline model
only has to include the system type spelled out in the guidelines?

 

William Mak, LEED Green Associate
Mechanical Design Engineer

EPSTEIN
Architecture
Interiors
Engineering
Construction

600 West Fulton Street
Chicago, Illinois 60661-1259

D: (312) 429-8116
F: (312) 559-1217
E: wmak at epsteinglobal.com
W:  <http://www.epsteinglobal.com/> www.epsteinglobal.com

þ Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.

 

From: James V Dirkes II, PE [mailto:jvd2pe at tds.net] 
Sent: Monday, February 28, 2011 3:14 PM
To: Will Mak; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] modeling baseboard in 90.1-2007

 

Dear Will,

 

All baseline systems have some sort of (non-baseboard) heating as part of
the system.  Baseboard would only be used for a Proposed system.

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Will Mak
Sent: Monday, February 28, 2011 3:48 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] modeling baseboard in 90.1-2007

 

Hello all,

 

I was trying to find some guidance on how we are suppose to model baseboard
systems on the baseline model for LEED submission. Are they treated like
preheat systems where we must simulate them to be the same on both the
proposed and baseline or is there some rule I’m not seeing in ASHRAE
90.1-2007?

 

Thanks!

 

William Mak, LEED Green Associate
Mechanical Design Engineer

EPSTEIN
Architecture
Interiors
Engineering
Construction

600 West Fulton Street
Chicago, Illinois 60661-1259

D: (312) 429-8116
F: (312) 559-1217
E: wmak at epsteinglobal.com
W:  <http://www.epsteinglobal.com/> www.epsteinglobal.com

þ Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110228/869f6b85/attachment.htm>


More information about the Bldg-sim mailing list