[Bldg-sim] existing envelope CIR
Will Mak
wmak at epsteinglobal.com
Mon Feb 28 06:38:27 PST 2011
>From my understanding, to even apply for LEED you need to meet ASHRAE 90.1-2004/2007 compliance for envelopes, etc?
William Mak, LEED Green Associate
Mechanical Design Engineer
EPSTEIN
Architecture
Interiors
Engineering
Construction
600 West Fulton Street
Chicago, Illinois 60661-1259
D: (312) 429-8116
F: (312) 559-1217
E: wmak at epsteinglobal.com
W: www.epsteinglobal.com <http://www.epsteinglobal.com/>
þ Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Marcus Sheffer
Sent: Monday, February 28, 2011 8:36 AM
To: 'Jackson, Alan'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] existing envelope CIR
The CIR is wrong and is in direct contradiction to Appendix G and the Energy Modeling Guide for LEED.
I have never seen a reviewer cite this CIR in a review.
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, sheffer at sevengroup.com <mailto:sheffer at sevengroup.com>
www.sevengroup.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jackson, Alan
Sent: Monday, February 28, 2011 9:26 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] existing envelope CIR
Is anyone aware of this CIR being upheld?
12/10/2008 - Credit Interpretation Request
The team is requesting that you please verify the meaning of the sentence in ASHRAE 90.1, Table G3.1 regarding baseline
envelope requirements for existing buildings.."For existing building envelopes, the baseline building design shall reflect existing
conditions prior to any revisions that are part of the scope of work being evaluated". Please confirm if this means that the walls, roof,
windows, etc for the baseline is to be modeled to match the existing conditions NOT according to the values in Table 5.5-1 thru 5.5-
8.
2/20/2009 - Ruling
If an existing envelope component is untouched, the baseline is as that component exists. However, if an existing component is
modified, the baseline needs to meet the requirements for alterations in Section 5.1.3.
It indicates that when modifying the existing envelope, the baseline needs to meet the minimum requirements of Chapter 5.
Have users in the group received comments from the reviewers when trying to model modified envelopes at the existing performance values, because all language regarding this issue other than the CIR indicate that existing envelopes get to be modeled at existing performance conditions regardless of any alterations.
Thanks
Alan Jackson, LEED AP
HVAC Project Engineer / BIM Team Leader
KlingStubbins
2301 Chestnut Street
Philadelphia, Pennsylvania
19103
P 215.569.2900, ext. 3380
F 215.569.5963
E ajackson at klingstubbins.com <mailto:jdoe at klingstubbins.com>
W www.klingstubbins.com <http://www.klingstubbins.com/>