[Bldg-sim] HVAC Equipment Sizing
Sandeep Kachhawa
sandeep.kachhawa at gmail.com
Wed Feb 16 07:01:20 PST 2011
yes the thermal mass of the building may lead to this sort of behavior, but
is it a general phenomenon? Further to my previous mail, there is no night
setback in my model and I am taking the same building for both the cases by
just changing the schedules accordingly
Regards
Sandeep Kachhawa
On Wed, Feb 16, 2011 at 8:13 PM, Michael A. Eustice
<MAEustice at htlyons.com>wrote:
> My best guess would be the pull-down cooling load. If you’re modeling
> the 12-hr building as 12 hours occupied and 12 hours unoccupied. The
> software may let the building temperature float way up outside of setpoint
> during the unoccupied hours. Then, when your occupied hours start, the
> equipment needs extra capacity to pull down the thermal lag of the building
> to meet setpoint in a reasonable timeframe. Make sense? Are you modeling
> it that way?
>
>
>
> Michael
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Sandeep Kachhawa
> *Sent:* Wednesday, February 16, 2011 9:33 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] HVAC Equipment Sizing
>
>
>
> Dear all
>
>
>
> I am comparing the epuipment sizing of a day time and a 24 hr office
> building on EnergyPlus. When I simulate the two while autosizing the hvac
> equipment, the Nominal Cooling Capacity (W) of the 24 hr building comes less
> than the day time building. Though the total energy consumption, as
> expected, of the 24 hr building is more than the 12 hr building, why
> the cooling capacity (equipment size) of the 24 hr building is lower than
> the 12 hr building. In my particular case, for a conditioned area of around
> 1600 m2, the cooling capacity for day time and 24 hr building is coming
> around 146 kW and 128 kW, respectively.
>
> What could be the possible reasons for such behaviour?
>
>
>
> Thanks
>
> Sandeep Kachhawa
>
> ------------------------------
> The information contained in this message is intended only for the personal
> and confidential use of the recipient(s) named above. If the reader of this
> message is not the intended recipient or an agent responsible for delivering
> it to the intended recipient, you are hereby notified that you have received
> this document in error and that any review, dissemination, distribution, or
> copying of this message is strictly prohibited. If you have received this
> communication in error, please notify HT Lyons immediately, and delete the
> original message.
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110216/1e12ff5d/attachment.htm>
More information about the Bldg-sim
mailing list