Dear Mr. Sharma,
You are correct that there are no outputs specific to the radiant loop objects or the "InternalSource" constructions that will give you a surface temperature. However, you should be able to grab any surface's temperature with:
Output:Variable,
SURFACE NAME,
Surface Inside Temperature,
Daily OR Hourly;
Regards,
Peter
____________________________________
Peter May-Ostendorp, EIT, LEED AP
PhD Candidate
University of Colorado at Boulder
College of Engineering and Applied Sciences
Building Systems Program
M: 970.426.8827
Please think before printing.
On Dec 29, 2011, at 2:31 PM, <bldg-sim-request at lists.onebuilding.org> wrote:
> Send Bldg-sim mailing list submissions to
> bldg-sim at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> bldg-sim-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> bldg-sim-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Bldg-sim digest..."
> <Today's Topics (1 messages).txt>
> From: Sachin Sharma <sachin5787 at gmail.com>
> Subject: [Bldg-sim] Radiant Floor Temperature in EnergyPlus
> Date: December 29, 2011 4:59:44 AM MST
> To: "'bldg-sim at lists.onebuilding.org'" <Bldg-sim at lists.onebuilding.org>
>
>
> Hi,
>
> I am modelling a radiant hydronic floor cooling system. I want to know the floor temperature report on daily or hourly basis of my conditioned zone. I have tried finding the option in Output:Variable object, but not able to find it. Can anyone help me out.
>
> Thanks,
>
> With regards,
>
> Sachin Sharma
> M.Tech Energy Engg.
> Department of Mechanical Engineering
> NIT Jaipur
> +91 9983912512
>
>
>
> <Digest Footer.txt>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111229/bd32b4ad/attachment.htm>
More information about the Bldg-sim
mailing list