[Bldg-sim] modelling of curtains

David BRADLEY d.bradley at tess-inc.com
Thu Dec 22 07:21:45 PST 2011


Leen,
  I would think that the approach would differ depending on whether the 
curtains were right up against the window or if they were in a doorway 
between two zones. I would also guess that there would be some 
differences in approach depending on what simulation tool you are using. 
In TRNSYS, curtains up against windows can be handled as a window 
shading device. For curtains separating two zones, you could model the 
opening as an adjacent window (using the virtual /open window 
properties), which would then allow you to define a shading device and 
pass solar radiation from one zone to the other. You can also define 
coupling airflow depending on whether the curtain is open or closed.
best,
  David

On 12/21/2011 15:25, leen peeters wrote:
> Dear all,
> regarding the modelling of curtains in a zone, I would like to know 
> what the general approach is. It seems logical to model a seperate 
> zone with an infiltration (to the main zone) of which the flow rate 
> depends on the opening or closing of the curtain. Mian issue is that 
> such an approach might affect the solar radiation into the main zone ...
> Leen
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111222/9f742d29/attachment.htm>


More information about the Bldg-sim mailing list