[Bldg-sim] Number of unmet hours
Nick Caton
ncaton at smithboucher.com
Mon Dec 5 15:16:25 PST 2011
Rathnashree and others,
I can further nail down the eQuest-specific procedural queries.
Summing the zone-level unmet hour reports (SS-R) can result in
"double-counting." I personally started out doing exactly that, but
eventually learned better =).
For the record, SS-R reports remain very useful for identifying &
isolating the spaces/systems involved in a high-unmet hour situation.
It's also worth noting the same totals for each zone & system are much
more easily reviewed under the 'Summary' tab under 'Air-side HVAC'
following a simulation.
Some discussion on the topic in the archives may be misleading for those
using eQuest version 3.64 and onwards. We used to follow a specific
"hunt and peck" procedure to correctly determine the number of unmet
hours using the "hours fans on" output in report SS-E. Users of 3.64
onwards can enjoy a much more simplified approach: Look to the summary
BEPS report!
Here is an excerpt from the BEPS report of a dummy file I have handy:
TOTAL SITE ENERGY 988.49 MBTU 39.5 KBTU/SQFT-YR GROSS-AREA
39.5 KBTU/SQFT-YR NET-AREA
TOTAL SOURCE ENERGY 2860.57 MBTU 114.4 KBTU/SQFT-YR GROSS-AREA
114.4 KBTU/SQFT-YR NET-AREA
PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING RANGE = 15.68
PERCENT OF HOURS ANY PLANT LOAD NOT SATISFIED = 0.00
HOURS ANY ZONE ABOVE COOLING THROTTLING RANGE = 6
HOURS ANY ZONE BELOW HEATING THROTTLING RANGE = 427
Here, you can clearly see the model has a total of 6 unmet cooling hours
and 427 unmet heating hours. Those are what some of us on the list have
coined "coincidental unmet hours," so that's to say there is no
double-counting involved. If this were the results of a model following
90.1 appendix G, one would need to identify and correct problems in the
model and/or system design to reduce that 427 figure to an acceptable
level.
Hope that helps clarify!
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Hintz,
Scott Fredrick. (KSC-ISC-4011)[URS Federal Technical Services,Inc.]
Sent: Monday, December 05, 2011 4:25 PM
To: Bishop, Bill; Rathna Shree; bldg
Subject: Re: [Bldg-sim] Number of unmet hours
Unmet hours for occupied hours only has been discussed but there was no
good consensus on exactly how to do this. So, yes, unmet hours are of
the entire (8,760) simulation and are building level, meaning one zone
or all zones unmet that hour is still just one unmet hour.
Trane CDS has a good document for combating unmet hours in TRACE 700. I
think it's probably generic enough to be used for any tool.
Scott Hintz
CEM, LEED-AP BD+C, BEMP
HVAC & Energy
Sustaining Systems Engineering (SSE)
Federal Technical Services
PO Box 21025, M/C: ISC-4011
Kennedy Space Center, FL 32899
Building: M6-493, Office: 1100H2
(321) 867-8533 office
(321) 867-5810 fax
scott.f.hintz at nasa.gov <mailto:henry.d.turner at nasa.gov>
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
Sent: Monday, December 05, 2011 9:03 AM
To: Rathna Shree; bldg
Subject: Re: [Bldg-sim] Number of unmet hours
Rathna,
The simulation covers 8760 hours, but this does not imply 8760 hours of
fan operation. I don't see anything in Appendix G that requires you to
prorate the 300 unmet load hours based on the schedules of building
operation. So, just stick with the 300 hour threshold.
I suggest you follow your four-step procedure (in eQUEST or other
DOE-2), except that I've never had unmet plant loads so I'm not sure how
I would take that into account. I disagree with Ashu - adding up all the
unmet hours in all SS-R reports can double-count (or more) coincident
unmet hours.
Regards,
Bill
<mailto:wbishop at pathfinder-ea.com>
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ashu Gupta
Sent: Monday, December 05, 2011 5:45 AM
To: 'Rathna Shree'; 'bldg'
Subject: Re: [Bldg-sim] Number of unmet hours
Hi Ratnashree,
You can directly see no of unmet hours for each system from SS-R report
and total number of hours (all systems) should not be exceed 300 hours.
Thanks!
Ashu
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rathna
Shree
Sent: Monday, December 05, 2011 3:59 PM
To: bldg
Subject: [Bldg-sim] Number of unmet hours
Dear All,
The following is the procedure i use to calculate unmet hours:
1) Percentage of Plant and system unmet is got from BEPU report.
2) The number of hours fan is on is got from SS-E report.
3) Percentage of system unmet(BEPU) multiplied by number of fan on
hours(SS-E) gives the Unmet hours.
4) Plant and system unmet together should not exceed 300 hours.
But as per ASHRAE 90.1, the 300hours of unmet is w.r.t. a simulation for
8760 hours. If the building is only 8 hours working 5 days a week, then
the fan on hours vary. Will the same 300 hours hold good for 3500 hours
of operation also.
The maximum percentage of Unmet for 8760 hours of operation is 3.4%
amounting to 300 hours. Do we have to take 3.4% of the total fan on
hours to calculate maximum unmet hours if the fan on hours is anything
other than 8760?
Please help.
Regards,
Rathnashree
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111205/7ffb3eb9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111205/7ffb3eb9/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1470 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111205/7ffb3eb9/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 21646 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111205/7ffb3eb9/attachment-0001.png>
More information about the Bldg-sim
mailing list