[Bldg-sim] ASHRAE 90.1 unmet load hours

Jim Dirkes jim at buildingperformanceteam.com
Fri Dec 2 09:53:45 PST 2011


Thanks, Michael.

You are correct about throttling range in E+, and I have already tinkered
with the ReportingTolerance.

I am aware that there seems to be no official  definition of "reasonable",
but presumed that there was a consensus and it was reflected in the default
E+ value.

Maybe not..

 

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: Rosenberg, Michael I [mailto:michael.rosenberg at pnnl.gov] 
Sent: Friday, December 02, 2011 12:19 PM
To: Jim Dirkes; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] ASHRAE 90.1 unmet load hours

 

Jim,

 

I think you are using E+, which does not have an input  throttling range. We
have found that loads not met are dependent on the E+ object
OutputControl:ReportingTolerances, which defaults to 0.2 deg. C ., which is
quite small. You might try increasing that to something more reasonable. 

 

Mike

 

 

 

__________________________

 

Michael Rosenberg, CEM, LEED AP 

Senior Research Scientist

ENERGY & ENVIRONMENT DIRECTORATE 

 

Pacific Northwest National Laboratory 

2032 Todd Street 

Eugene, OR 97405 

(541) 844-1960 

 <mailto:michael.rosenberg at pnl.gov> michael.rosenberg at pnnl.gov 

 <http://www.pnl.gov/> www.pnnl.gov

 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jim Dirkes
Sent: Friday, December 02, 2011 6:33 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1 unmet load hours

 

Dear Forum,
Feedback requested, please!  I've looked at some past posts on this general
topic and think I am asking about aspects not previously discussed..

>From previous posts and my own understanding:

.         If one or more zones is not meeting its setpoint in a given hour,
you have 1 unmet load hour.  If 500 zones all fail to meet their setpoint in
one hour, it's till one unmet load hour.

.         Add all such hours in a year to obtain your total unmet load
hours, which cannot exceed 8,760.

I am now modeling a hotel with:

.         "Massive" wall elements in the lower floors with moderate amounts
of glass, "lightweight" construction in the upper floors with a lot of glass

.         Occupancy schedules that are all over the map for Office, Assembly
/ Meeting Rooms, Kitchen & Restaurant, and Guest Rooms

.         Individual HVAC systems for almost every occupancy type.

.         Presentation to all points of the compass, especially the Guest
Tower, which is a 16-sided (roughly cylindrical) tower

This model is making my life very difficult trying to get unmet load hours
below 300!  As I think about why that is happening, it strikes me that the
combination of mass, schedules and orientations are spreading the unmet
loads around to different hours than is normal for many buildings.  Can any
of you share your thoughts about that perspective?

Thanks!

ASHRAE 90.1-2007

unmet load hour: an hour in which one or more zones is outside of the
thermostat setpoint range.

 

 

Description: Description: BPT BizCard JVDII Updated

 

The real measure of a person's wealth is how much they're worth after losing
all their money.

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111202/f438e15c/attachment.htm>