Hi John!
I think the short answer is bump up your ACH for the room "higher than
normal." Trying to quantify any more specifically is probably a
fruitless endeavor - way too many variables in play...
Fundamentals 2009 has a fuzzy thing or two to say about to what extent
door infiltration ordinarily affects whole-building infiltration
(6-22%):
Windows and doors (6 to 22%; 15%). More variation in window
leakage is seen among window types (e.g., casement versus
double-hung) than among new windows of the same type from different
manufacturers (Weidt et al. 1979). Windows that seal by
compressing the weather strip (casements, awnings) show significantly
lower leakage than windows with sliding seals.
That may help you establish a ceiling to what's likely.
There's also a longer discussion relating that "rough" ACH estimations
have to be made in design for the purposes of sizing HVAC equipment on
(page 16.29)... Examples provided for some smallish (80-150SF)
vestibules range from 0.5 to 2.0 ACH, but importantly illustrate the
process is necessarily somewhat arbitrary. The point they're making is
there are a bunch of hard to measure/estimate variables in play to
determine actual ACH, from height to hourly temperature differentials to
wind pressures.
Throw a "higher" number at it, at least until someone can source/share
some table of "better guesses" =).
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of John Eurek
Sent: Wednesday, August 24, 2011 2:06 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Frequently used door
I'm trying to model a small building (600 square ft) which will be used
to inspect cars. The worker will frequently be using the door. Logic
would say that the equipment sizing and design would be different from a
similar building with a door which is not frequently used.
The building is so small that leaving the door open for a short time
could result in a complete air change in a short time.
I use Trace 700. Does anybody have any methods to account for high door
usage to size the equipment? Trying to make up an energy model will be
difficult also.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110824/d5192095/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110824/d5192095/attachment.jpeg>
More information about the Bldg-sim
mailing list