Rohini,

 

We require that models are calibrated following ASHRAE Guideline 14 for
projects that participate in several major (hundreds of buildings in the
pipeline) modeling-based incentive programs in North East. To support this
requirement, we developed a spreadsheet-based tool to verify achieved
calibration (via pass/fail flag). Statistical calculations and tolerances in
the tool are largely based on Guideline 14, which we had to tweak in few
places to better adapt it to real life scenarios that we ran into (e.g.
stored fuels with no clean monthly usage data, etc.). The process also uses
ETRACKER software, a free weather normalization tool from University of
Dayton http://academic.udayton.edu/kissock/http/Weather/default.htm. The
above mentioned incentive programs rely on network of approved providers
that are required to use the tool to document incentives. If you'd like to
get the tool, feel free to email me off the list (the file is rather large).


 

Thanks,  

 

Maria 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of R B
Sent: Friday, April 29, 2011 10:50 AM
To: Katherine Louman-Gardiner
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest - Model verification

 

There is a ASHRAE guideline that outlines the metrics for deciding when the
model is calibrated - ASHRAE guideline 14. Also it is alluded to by the RMI
modelling workshop slides. The CVRMSE is around 10%, and the monthly ERR is
15%. I usually look at these numbers for electric and gas separately.

How many people follow the ASHRAE guideline for calibration and are there
any other metrics out there?

 

Thanks

-Rohini

On Thu, Apr 28, 2011 at 12:48 PM, Katherine Louman-Gardiner
<klgardiner at flowgroup.ca> wrote:

Hi All,

Our client would like us to produce an eQuest model that

a)      Can be easily adjusted to include current and recently recorded
weather data

b)      Can be easily adjusted to reflect space occupancies and lighting
loads

c)       Will reflect the actual building energy usage to within 1%

Do any of you have experience trying to validate models like this?  

My concern is that models are approximations, and will not account for small
changes in occupancy, outdoor weather, etc.  

I guess my questions are these:

1)      Even if I manage to put in daily occupant and fan schedules based on
actual use, will the model be accurate enough to take me within 1%?

2)      We have been asked to remove plug loads (both for consumption
purposes and cooling loads).  Will this be too big of an assumption to get
any accuracy out of the model in the future?

3)      How do I modify the weather input file?

4)      Are there any other ideas I'm missing that will help us validate a
model as an absolute measure of actual building energy consumption?

Thank you for your help,
Katherine

 

Katherine Louman-Gardiner, EIT

Mechanical Engineer

 


_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110429/37a59f68/attachment.htm>


More information about the Bldg-sim mailing list