[Bldg-sim] Core and Shell Office Modelling
Jaigath Chandraprakash
cjaigath at yahoo.com
Thu Apr 7 07:51:23 PDT 2011
Thank you James.
That is my next question. Where to base the fcu efficiency? You said Appendix G
but the constant volume fans are for dx units, will it be acceptable? Should I
use system 1&2 formula or system 3&4?
________________________________
From: James Hansen <JHANSEN at ghtltd.com>
To: Shanta Tucker <shanta.tucker at atelierten.com>; Jaigath Chandraprakash
<cjaigath at yahoo.com>; bldg-sim at lists.onebuilding.org
Sent: Thu, April 7, 2011 10:31:03 PM
Subject: RE: [Bldg-sim] Core and Shell Office Modelling
To further what Shanta said: unless you have a legally binding lease agreement
that lists specific efficiencies of the fan coil units that the tenants must buy
(or a requirement that the tenants must purchase FCUs that match the basis of
design on the contract drawings), then I believe the fan power of those FCUs
must unfortunately match the Appendix G requirements. In other words, you can’t
model an ECM motor tenant FCU in your proposed design unless there is some
enforceable document that requires tenants to purchase them in this arrangement.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com
From:bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Shanta Tucker
Sent: Thursday, April 07, 2011 10:19 AM
To: Jaigath Chandraprakash; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Core and Shell Office Modelling
Hello Jaigath,
My suggested answers follow your questions.
1. Does that mean I will be modeling only the common since it only the areas
that were designed? No. You must model the whole building and site.
2. Do I need to also include the tenant areas? Yes, include the tenant spaces.
3. Since the tenant areas have FCU pipe provision, do I model it as FCU or do I
have to model it as system 6 which is my baseline case? You may model the tenant
spaces with FCU’s in the proposed model so long as you have an engineering
drawing for a typical floor showing this; if you don’t have this I suggest that
you ask for it. If that is not possible to obtain, perhaps a narrative from the
engineer of record or the tenant lease would suffice, but I’m not 100% sure if
it would. In my opinion, you’ll need to provide some documentation that the
tenants must install the FCU’s in order to help the GBCI reviewers understand
the argument why you are modeling FCU’s and not system 6.
--
Shanta Tucker
Atelier Ten
From:bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jaigath
Chandraprakash
Sent: Thursday, April 07, 2011 7:21 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Core and Shell Office Modelling
I am simulating a core and shell office building with system 6 for my baseline.
The design case is a two pipe fan coil units at common areas and all tenants
will have chilled water pipe provision for them to tap their fan coil units.
Based in CS Appendix 6 under step 1, model the HVAC system as described in the
design documents. My question is:
1. Does that mean I will be modeling only the common since it only the areas
that were designed?
2. Do I need to also include the tenant areas?
3. Since the tenant areas have FCU pipe provision, do I model it as FCU or do I
have to model it as system 6 which is my baseline case?
Thank you all in advance.
Jaigath
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110407/54c71b95/attachment.htm>
More information about the Bldg-sim
mailing list