[Bldg-sim] Parking Structure LEED Energy Model
Nick Caton
ncaton at smithboucher.com
Wed Sep 8 15:36:11 PDT 2010
Hi Brian,
The 90.1 User's manual Table G-B, which I've come to regularly reference
for LEED projects instead of trying to force 25% process loads into my
models, lists parking garages as having a receptacle power density of
"NA" (distinct from the other entries). If you are unaware of any
specific receptacle loads to include, I'd infer from this and the
accompanying text that you're not expected to model any.*
Your process loads overall would still include any garage ventilation
fans, elevators, mechanical bollards, moving walkways, escalators, car
washes, mechanized street sweeping monkeys and so on.
~Nick
* Small disclaimer: The review process being what it is, nobody can
guarantee a reviewer that will force their personal interpretations down
your throat won't be assigned to your project. The best you can do is
to document plainly any interpretations you have to make, and
cite/reference as you must to make your case clearly rational.
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Brian Tysoe
Sent: Wednesday, September 08, 2010 3:57 PM
To: 'bldg-sim at lists.onebuilding.org'
Subject: [Bldg-sim] Parking Structure LEED Energy Model
Hi,
I am working on a preliminary LEED energy model for a six-story 500,000
square foot parking structure. The parking area is unheated. The major
energy usage is lighting; followed by heating of stairs, elevator
lobbies, storage, etc.
Do I have to consider a 25% process load? What would that be?
Thanks,
Brian Tysoe M.A.Sc., P.Eng., LEED AP
Mechanical Engineer
MCW Consultants Ltd. <http://www.mcw.com>
600-156 Front Street West
Toronto, ON M5J 2L6
Phone 416-598-2920
Fax 416-598-5394
This e-mail may be privileged and confidential. Any unauthorized use is
strictly prohibited. If you received this e-mail in error, please
contact the sender directly.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100908/a96134b1/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100908/a96134b1/attachment.jpeg>
More information about the Bldg-sim
mailing list