[Bldg-sim] Hot-Water Supply Temperature Reset in DOE2.1e
Chris Jones
cj at enersave.ca
Wed Oct 20 13:14:21 PDT 2010
DOE2.1e from Hirsh uses the HW-SUPPLY-RESET = LOAD-RESET
"LOAD-RESET indicates that the HW-SUPPLY-T will
be reset so that one hot-water coil valve is
fully open. All other hot-water coil valves will
modulate as required to maintain the supply air temperature set-point."
At 11:36 AM 20/10/2010, Eric Zagorski wrote:
>Content-Language: en-US
>Content-Type: multipart/alternative;
> boundary="_000_4F46B8EDBEE3424491F1CE6FBE6C33FE045B7Femeserver02_"
>
>Hi All,
>
>I am currently modeling a building in DOE2.1e
>and am trying to comply with ASHRAE 90.1-2007
>section G3.1.3.4 which states that:
>
>Hot-water supply temperature shall be reset
>based on outdoor dry-bulb temperature using the
>following schedule: 180°F at 20°F and below,
>150°F at 50°F and above, and ramped linearly
>between 180°F and 150°F at temperatures between 20°F and 50°F.
>
>DOE2.2 allows you to model this in the
>CIRCULATION-LOOP command, but DOE2.1e does not
>recognize that code-word. Does anyone know how
>to incorporate hot-water temperature reset in DOE2.1e?
>
>Thanks,
>
>Eric Zagorski
>EME Group | Consulting Engineers
>159 W. 25th Street
>New York, NY 10001
>Tel: (212) 529-5969 x330
>Fax: (212) 529-6023
><http://www.emegroup.com>www.emegroup.com
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel. 416-203-7465
Fax. 416-946-1005
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101020/e417e5d6/attachment.htm>
More information about the Bldg-sim
mailing list