Exception a of G3.1.1 looks at your proposed systems and has the noted 20,000 sf criteria.
Exceptions b & c are tied to thermal zones and are not tied to your proposed system configuration.
The planned system boundaries alone are not sufficient to trigger a separate lookup in table G.3.1.1A.
Often the mapping of system to zones is different between proposed and baseline model.
Regards,
Paul Riemer
Dunham


From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Carol Gardner
Sent: Thursday, October 14, 2010 9:39 AM
To: Rob Hudson
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Interpretation of Table G-A in ASHRAE 90.1 2007

Hi Rob,

If the systems serve distinctly different uses that comprise more than 20,000 sf you are fine. Otherwise, I would use the predominant heat source. It will be interesting to hear others opinions.

Carol
On Thu, Oct 14, 2010 at 6:29 AM, Rob Hudson <rdh4176 at gmail.com<mailto:rdh4176 at gmail.com>> wrote:
Scenario:
I have an "intermediate" sized building (25,000 to 150,000 sqft) with several systems in it.  can each system be determined separately or should each by a System type 5/6 depending on Heating source?  I would like to label some small systems as a type 3/4 and some as type 5/6 depending on the area that is served by the system.

thanks for any opinions that people would like to share.

--
Rob Hudson

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>



--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101014/fd054f2a/attachment.htm>


More information about the Bldg-sim mailing list