[Bldg-sim] Automatic Lighting Shutoff MandatoryProvisionQuestion

Jeremy Poling jpoling at epsteinglobal.com
Wed Oct 6 15:01:52 PDT 2010


Nick,

 

Table G3.2 by itself also has to cover all possible situations, but it
is also only to provide credit for controls in addition to the mandatory
provisions.  I'll explain my view on those two issues separately. 

 

The intent of 9.4.1.1 from the 90.1 Users Manual is to ensure all
buildings "have an automatic control device that is capable of turning
off lighting in all spaces without human intervention."  This ensures
energy savings when the building is unoccupied.  Since occupants leave a
space during the day for various reasons, 9.4.1.2 exists to ensure that
unoccupied spaces during occupied hours have a means to save energy by
turning off the lights, either automatically or manually.  In addition,
that same device (if capable) can serve as the override (for safety
reasons) to turn lighting on in the space during unoccupied hours -
another mandatory provision of 9.4.1.2.  The way I read it, an occupancy
sensor alone cannot comply with both mandatory provisions because
9.4.1.2 requires an override to the automatic controls required by
9.4.1.1.  If the occ sensor is installed to comply with 9.4.1.1 and no
means is provided to override the control (such as a manual switch),
then compliance with 9.4.1.2 has not been demonstrated.  Once I have
satisfied 9.4.1.1 and 9.4.1.2 and only then can I look to Table G3.2 for
credit for automatic controls.  That is what Table G3.1(6)(g) says.

 

G3.2(1) only applies to buildings less than 5,000SF and non-24-hour
operations and gives 0% credit to larger buildings.  This is in line
with 9.4.1.1 that requires whole building control for buildings larger
than 5,000SF but not for those smaller.  G3.2(2) and G3.2(3) provide the
exact same credit for only an occ sensor or for an occ sensor and
programmable timing device (15% for buildings less than 5,000SF and
non-24-hr, 10% for others).  This "estimates" the savings from
compliance with 9.4.1.1 at approximately 5% for buildings larger than
5,000SF.  The 24-hour operation comment in G3.2 is due to exception (a)
to 9.4.1.1 since whole building control is not required for 24-hour
operations.

 

A situation I could see using G3.2(3) would be one of the more high-tech
security systems.  If the security system is tracking occupancy via
security card swipe-in/out records, then it would be capable of
determining that the building is unoccupied.  It could send a signal to
a relay panel to turn of the lighting.  That would comply with
9.4.1.1(c).  At that point, if every space were designed with manual
controls (except the three that require automatic controls) then the
manual controls would comply with 9.4.1.2.  If a time clock and
occupancy sensor were installed in addition, that would allow the credit
from G3.2; however, as you pointed out, no additional efficiency would
be gained by the combination of the two that was not achieved by the occ
sensor alone and indeed, Table G3.2 does not provide any additional
credit for installing both in this case where neither would be required
for compliance with the mandatory provisions.

 

I think it is an order of reading the code issue - since the mandatory
provisions come first, both 9.4.1.1 and 9.4.1.2 must be satisfied before
credit can be taken.  If the building only has a time clock, in that
typical office - there needs to be a local control for compliance with
9.4.1.2.  If that office has a switch that can function as an override
to the time clock AND a local control device, then that occ sensor would
indeed be eligible for the 10% credit.  But if the office just has the
time clock and the occ sensor - no other devices, then I don't see any
other way that 9.4.1.2 is satisfied except by the occ sensor, meaning it
is part of the mandatory provisions and not eligible for credit under
Table G3.2.

 

A single occ sensor with no other controls for the lighting in a space
(in buildings larger than 5,000SF) cannot comply with 9.4.1.1, 9.4.1.2
and earn credit under Table G3.2 since table G3.2 is for controls in
addition to the minimum.  Going back to the original question, I think
the issue arises somewhat from reviews only recently "cracking down" on
this part of the code...

 

Thoughts?

 

Separately, I also agree with the last comments - Baseline LPD is left
alone, always.  Table G3.2 only applies to the proposed design and is a
prescriptive alternative to having to use G2.5 Exceptional Calculations.

 

JEREMY R. POLING, PE, LEED AP
Associate Vice President,

Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability

EPSTEIN
Architecture
Interiors
Engineering
Construction

Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.

 

From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Wednesday, October 06, 2010 9:48 AM
To: Bishop, Bill; Jeremy Poling; R B
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Automatic Lighting Shutoff
MandatoryProvisionQuestion

 

Jeremy, 

 

Bill's condensed my thoughts very well.  This logic is further supported
by Table G3.2:

 

If, for your "typical office" case, one needs both a local occupancy
sensor and a timeclock on the circuit to demonstrate a savings in the
proposed model, why would table G3.2 have distinct lines for "occupancy
sensor and programmable timing control" as well as simply "occupancy
sensor?"  As you've noted, this table exists for the sole purpose of
doling out credit for proposed models, so there's no answer other than
one may be able to claim credit for occ. sensors without timer control.

 

More to the point, and as Bill notes - there's no savings gained with a
timeclock in combination with an occ. sensor that can't be achieved by
an occ. sensor alone (that's how I think of it anyway).  An occ. sensor
will however save you energy over a timeclock alone as you'll achieve
shutoff periods during working hours.  That's probably why the LPD
reductions in the two lines mentioned above are identical.  For these
reasons, I think we can consider occ. sensors alone to be "in addition
to" the minimum automatic shutoff requirements - inferred to be a
timeclock alone.  I reckon you can take the LPD credit in those spaces.

 

To your classroom example:  Yes, I've regularly interpreted spaces like
classrooms with automatic shutoff and multi-scene controls to be
qualified for a LPD reduction due to the corresponding exemption in
9.4.1.2.

 

Hope that helps!

 

~Nick

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com] 
Sent: Wednesday, October 06, 2010 8:56 AM
To: Jeremy Poling; Nick Caton; R B
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Automatic Lighting Shutoff
MandatoryProvisionQuestion

 

Jeremy,

 

I agree with Nick's explanation to Jaigath, below. A 10% LPD credit can
be taken in spaces that have occupancy sensors, except where occupancy
sensors are required (classrooms etc. per 9.4.1.2). It would make no
sense to allow energy savings only for spaces that have both time clock
and occupancy controls, since a space with both controls would provide
no additional energy savings over an occupancy sensor alone.

 

I also agree with Nick's comment to Rohini. Leave the baseline LPD alone
(turning lights off during unoccupied hours using the same schedule in
baseline and proposed) and take the 10% credit in the proposed where
applicable.

 

Regards,

Bill

 

William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP

Mechanical Engineer

 

134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005

wbishop at pathfinder-ea.com

www.pathfinder-ea.com

P   Sustainability - the forest AND the trees. P

 

________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jeremy
Poling
Sent: Wednesday, October 06, 2010 12:52 AM
To: Nick Caton; R B
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Automatic Lighting Shutoff
MandatoryProvisionQuestion

 

We just had a pretty in-depth discussion on this internally also - local
implementations of the code (for example, Chicago Building Code) have
added some confusion.  To add to what Nick said, the credits in table
G3.2 are only referenced in the lighting requirements in Table G3.1 and
are specifically listed for use in the proposed model for controls that
are not already required by the mandatory provisions of Section 9.  I've
always found it ironic that a Section G3.2 doesn't exist even though a
Table G3.2 does...but I digress...here is where we arrived internally:

 

Section 9.4.1 has 4 main parts - Whole building control, individual
space control, exterior lighting control and additional mandatory
controls.

 

-        9.4.1.1 requires an automatic whole building control capable of
shutting off lighting (with override capabilities allowed) for the
entire building based on either (a) time clock signal, (b) occupancy
sensors, or (c) some other control signal (like a BMS).  This applies to
all buildings over 5,000 SF.

-        9.4.1.2 requires an individual control for all spaces, either
manual or automatic.  For specific space types, automatic controls are
required: classrooms (except shop classrooms, laboratory classrooms, and
preschool - 12th grade classrooms), conference/meeting rooms, and
employee lunch and break rooms UNLESS those rooms have multiscene
control in which case they are also exempt from the automatic
requirement.  All other spaces are not required to have automatic
controls and can have either manual or automatic controls.  In addition,
those spaces where automatic controls are mandatory are NOT required to
be connected to other automatic lighting shutoff controls (i.e. the
whole building controls required by 9.4.1.1)

-        9.4.1.3 requires photocell or astronomical time clock control
of site lighting (with some nuances, but this is a safe simplification
of the requirements).

-        9.4.1.4 requires a number of specialty lighting installations
to have controls - most applicable to LEED is the requirement for all
task lighting to have an individual control.

 

The way I simplified this for our engineers is the following: any and
all spaces will have 2 levels of code-required control.  The first will
comply with 9.4.1.1 and the second will comply with 9.4.1.2.  As an
example, for a typical private office our engineers have been using wall
devices that have an occ sensor with a manual control.  If that is the
only controls that cover the private office, then the occ sensor
complies with 9.4.1.1 and the manual switch complies with 9.4.1.2; no
credit from Table G3.2 would be allowed since both control methods are
required by 9.4.1.  Now, if there is a time clock in the building and
the private office were connected to the time clock with the same wall
device the situation would be different: the time clock would comply
with 9.4.1.1 and the manual switch would comply with 9.4.1.2 leaving the
occupancy sensor as an additional control, eligible in Table G3.2 for a
10% LPD credit against the PROPOSED LPD factors.  For a classroom in a
community center, if the lighting is setup for multiple purposes and the
space is on the building time clock, then you just have compliance with
9.4.1.2 and 9.4.1.1 respectively.  If you put in an occ sensor (some
control logic required due to the multiscene) then you can take credit
for that sensor in Table G3.2.

 

I'm curious what you two think of this interpretation?

 

We even went so far in our discussion to look literally at the way
9.4.1.1 is worded and I believe that since the word "either" does not
imply mixed compliance then any given building must comply entirely with
one of the three options, not a mix of two.  Say a time clock for common
spaces with occ sensors for tenant leased space, for example, would not
comply with the most strict reading of the code.  That is quite literal,
but I've had code reviewers who have read other codes that literally
before...

 

JEREMY R. POLING, PE, LEED AP
Associate Vice President,

Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability

EPSTEIN
Architecture
Interiors
Engineering
Construction

Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Tuesday, October 05, 2010 10:40 AM
To: R B
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Automatic Lighting Shutoff Mandatory
ProvisionQuestion

 

Rohini,

 

While it's a minor point, I'd only caution that my "hard and fast rule"
is pretty much a directly from Table G3.1.6:  "No automatic lighting
controls ... shall be modeled in the baseline building design..."  That
said, if I were a reviewer I wouldn't have a problem with your approach.

 

While modeling occ. sensors in both cases would help the EUI of the
proposed model, not modeling occ sensors in both cases will mean your
baseline and proposed  HVAC systems have to deal with extra internal
loads, so presuming you have a better HVAC system in the proposed model,
I'd intuitively assume if anything a classroom-heavy school/university
might do better to not model occ. sensors in each model... I guess if
the results bear it out, go with the flow though =).

 

~Nick



 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: R B [mailto:slv3sat at gmail.com] 
Sent: Tuesday, October 05, 2010 10:23 AM
To: Nick Caton
Cc: Jaigath Chandraprakash; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Automatic Lighting Shutoff Mandatory Provision
Question

 

I actually take the credit for occ. sensor in both the baseline and
proposed case for such spaces that have a mandatory requirement for
occupancy sensor (e.g. classroom). The advantage is your total energy
consumption is slightly less, so when you are in border line cases where
you are ever so slightly less than the required percentage points for
the next level of points it helps. Much more advantageous to do it this
way when you are doing a school/university building.
-Rohini

Rohini Brahme, Ph.D, LEED AP
Building energy analysis, tool development, and training
Dallas/Fort Worth, TX 

On Tue, Oct 5, 2010 at 9:06 AM, Nick Caton <ncaton at smithboucher.com>
wrote:

The hard and fast rule I follow is that baseline LPD's are never to be
messed with.  Any and all credit taken for lighting controls is a
deduction of LPD (or sufficiently documented schedule adjustment, I
suppose) in the proposed case. 

 

It can get confusing, but in specific spaces (i.e. classrooms), 9.4.1.2
may require occ. sensors.  In such a case, I don't take a credit in the
baseline (see hard/fast rule above), but instead remove the credit
otherwise taken for that space in the proposed case.    

 

~Nick



 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com
<http://www.smithboucher.com>  

 

From: Jaigath Chandraprakash [mailto:cjaigath at yahoo.com] 
Sent: Monday, October 04, 2010 8:32 PM
To: Nick Caton; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Automatic Lighting Shutoff Mandatory Provision
Question

 

Thank you very much Nick. I really appreciate your help on this.

 
I really got confused with this when I got a commnet recently saying
that the "baseline case per section 9.4.1.2 were not modeled" and was
asked to revised the baseline. So I ended up with no savings. This is in
conflict with Table G3.1.6 that you have pointed out which says that No
automatic lighting controls shall be modeled in the baseline building
design. 

 

Does it mean that I am wrong when I applied also 10% savings to my
baseline? This is where I got confused since 9.4.1.1.b also mentions
occupant sensor that shall turn lighting off within 30 mins of occupant
leaving the space. 

 

 

 

________________________________

From: Nick Caton <ncaton at smithboucher.com>
To: Jaigath Chandraprakash <cjaigath at yahoo.com>; 
bldg-sim at lists.onebuilding.org
Sent: Mon, October 4, 2010 10:38:08 PM
Subject: RE: [Bldg-sim] Automatic Lighting Shutoff Mandatory Provision
Question

Jaigath,

 

Appendix G allows us to take credit for automatic controls in addition
to (beyond) what's required in 9.4.1 for minimum compliance.  One of the
options here is to have programmable (time-of-day) shutoff for interior
lighting circuits, and you can infer from between Table G3.1 and G3.2 of
Appendix G that baseline models are taken to feature only such timeclock
controls for automatic shutoff.  Further, it's taken that the lighting
scheduling being kept identical between the proposed and baseline
adequately reflects the minimum requirements, so you aren't supposed to
try to explicitly model the programmable shutoff.  

 

If you have occupancy sensors throughout a building which only requires
programmable shutoff, that's an example of having automatic controls
beyond what 9.4.1 requires - and you'd get to take 10% off your proposed
LPD in all spaces where such short-term shutoff isn't already required
(per following section 9.4.1.2).

 

Note Table G3.2 also has a corresponding distinction between building
smaller than and larger than 5,000ft2 - offering more credit for
buildings using a means of automatic shutoff where no such controls are
even minimally required.

 

~Nick

Error! Filename not specified.

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: bldg-sim-bounces at lists.onebuilding.org [mailto:
bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jaigath
Chandraprakash
Sent: Monday, October 04, 2010 9:01 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Automatic Lighting Shutoff Mandatory Provision
Question

 

Hello All,

 

I am confused on the mandatory provision 9.4.1.1 which states that
building larger than 5000 ft2 shall have automatic control device. Does
it mean that mid-rise and high rise building cannot claim for credit in
occupancy sensors shown in Table G3.2 because their GFA is more than
5000 ft2 and only small office can claim for this credit? I am sure I am
not interpreting this section correct since from what I read, other
modelers  are claiming for savings for buildings with more than 5000 ft2
area for occupancy sensors even if mandatory requirements states that
this is required which means baseline building will also have occupancy
sensors.

 

Can someone correct me on this? 

 

Thank you,

 

 

C. Jaigath 

 

 


_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101006/9f146519/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101006/9f146519/attachment.jpeg>


More information about the Bldg-sim mailing list