[Bldg-sim] Adjusting Capacity for Unmet Cooling
Nick Caton
ncaton at smithboucher.com
Fri Nov 19 14:56:34 PST 2010
Hi Michael,
I’d like to offer a quick heads up – your interpretation of what 90.1 has to say regarding addressing unmet hours is spot on and well-stated, no disagreements here. Neeraj however is indirectly making a pretty valid point that I’d hate for anyone to miss…
If you only ever approach addressing unmet hours by bumping the oversizing factors, you may well be missing something critical. I for one was in this train of thought when I started out. To the letter of the standard, indeed this is all we’re *prescribed* to do to remedy the situation, but this approach will not always work, and may result in baseline models with a very skewed performance – suffice it to say skewed is not always a *good* thing, even if it does make your performance numbers look good.
Whenever I have unmet hours, I’ve learned through others on these lists to investigate the “why” and “when” of those unmet hours as a first step. More often than not, unmet hours in my models, when they do occur, have nothing to do with lacking heating or cooling capacity – fan (airflow) scheduling conflicts, thermostat setpoints and unrealistic deadbands are the primary culprits. The systems effectively aren’t running as frequently or for a duration as they should be.
When this is the case, and I can assure Neeraj is not alone in this experience, fluffing the oversizing factor may appear to “remedy” the issue, but often as not may *not* be enough to pull your baseline/proposed models into the prescribed requirements for unmet hours. In some cases, you might even make the situation worse. I’m pretty sure the spirit of the standard, by specifying a maximum number of unmet hours, is to allow both the proposed and baseline systems to run when they need to satisfy the loads
For whatever combination of reasons, and luck may be a part of it, it has been a long while since I’ve created an autosizing 90.1 baseline model whose unmet hours did not ring in at either zero or the single digits, and as such did not require any adjustments. I personally feel this has had a lot to do with understanding the mechanics behind what defines and can cause an unmet hour – as you’re getting at with consideration to drift points.
As you say, future versions of 90.1 may be more nuanced, but I personally feel the manner in which unmet hours are currently addressed does a disservice to those aspiring to be quality energy modelers – one can easily be misled to believe an unmet load hour is a problem in and of itself with an easy “fix,” without recognizing it’s really a symptom of a problem... bumping capacities without first addressing the cause of unmet hours is something like a doctor only giving you a band-aid for a cut when what you need is a tetanus shot!
It may be worth mentioning that my experience is dominantly within the world of eQuest/DOE2. I would not be surprised to find other engines/software have varying “typical” causes of unmet hours.
Anyway, that’s my two cents, for what it’s worth =) – hope it might help lead others along the path!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Michael Collarin
Sent: Friday, November 19, 2010 1:46 PM
To: Nearedge; cjaigath at yahoo.com
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Adjusting Capacity for Unmet Cooling
Neeraj, it is in fact the contrary.
ASHRAE 90.1-2007 Appendix G requires you to model Baseline Airflow Rate using a 20-degree F temperature difference between the supply air and room air temperatures. Therefore, if your room set point is 75F for cooling, set your cooling leaving air temperature to 55F and vice versa for heating; 72F heating set point requires a 92F leaving air temperature. This establishes your CFM airflow within the model. Do not vary these to adjust unmet hours.
If you have unmet heating or cooling hours (over 300 or greater than 50 between baseline and proposed), you may incrementally adjust the baseline cooling and heating capacities (originally oversized 15% and 25% respectively) accordingly to reduce the overall unmet hours (below 300) or the difference between baseline and proposed (within 50).
Before taking this step, be sure to look at your thermostat drift points. If the cooling set point is 75, but the cooling drift point is 84, when the space is unoccupied this would allow the space to move toward 84 degrees. When the space becomes occupied and the simulation tries to cool to 75, the system will not be able to achieve this within the allotted time (1 hour) and you will have an unmet cooling hour.
There are some changes to ASHRAE 90.1-2010 that will effect unmet hours, but for the time being, if you are modeling a project using 2007 or 2004, this method should help you eliminate the unmet hours.
Regards,
Michael M. Collarin, EIT, LEED AP BD+C | Elm Engineering, Inc. | 212 S Tryon St | Suite 1375 | Charlotte, NC 28281
PHONE 704-335-0396 Ext. 108| FAX 704-335-0399 | www.elmengr.com <http://www.elmengr.com/>
From: Nearedge [mailto:near_ej at yahoo.com]
Sent: Friday, November 12, 2010 12:51 AM
To: cjaigath at yahoo.com
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Adjusting Capacity for Unmet Cooling
Hello Jaigath,
Using the performance rating method (PRM), in my experience it is usually an issue of low supply CFM.
Correct me if I am wrong but on the contrary I think that ASHARE baseline PRM fixes the cooling and heating capacities to 1.15 and 1.25 respectively and the user is allowed to bump up the supply CFM in increments if necessary.
I have a feeling that the issue of unmet load hours has been discussed many times before -- so, the archives will be a good resource as well.
Best,
Neeraj
Neeraj Kapoor
t: +91.99581.70018
e: neeraj[at]kalpakrit[dot]com
Kalpakrit Sustainable Environments Pvt. Ltd.
www.kalpakrit.com
Office Address:
610-A Udyog Vihar, Phase-5,
Gurgaon, Haryana - 122016
t: +91.124.430.9490/ 1/ 2
f: +91.124.430.9493
Registered Address:
101 Anupam Apartments,
Mehrauli-Badarpur Road,
New Delhi - 110068
On 11-11-2010 10:30, Jaigath Chandraprakash wrote:
Hello All,
I would like to know how other increase their baseline capacity when they have unmet load. I have a PSZHP system and in one system, I got more than 400 hrs unmet load. I usually just increase the TR cooling capacity until I get a lower unmet load but in this case, I think the unmet load is due to low supply cfm. Is it ok to adjust also the supply fan cfm? I am thinking that G3.1.2.2 only requires me to adjust only the cooling capacity. Do others adjust both cfm and cooling load?
Thanks,
Jaigath
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101119/4c57133a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101119/4c57133a/attachment.jpeg>
More information about the Bldg-sim
mailing list