This is the approach i previously took. i got review comments back and
wanted to double check to make sure before i resubmitted.
thanks,
On Fri, Nov 12, 2010 at 10:00 AM, Bishop, Bill <wbishop at pathfinder-ea.com>wrote:
> Rob,
>
>
>
> Generally, I combine all the spaces served by a single VAV box into one
> thermal zone for modeling purposes. The ASHRAE 90.1 User’s Manual, p.G-19
> has reasonable guidance on defining “thermal blocks”. Where HVAC zones have
> been designed, zones can be combined into thermal blocks for modeling
> purposes when all these conditions are met (paraphrasing here):
>
> 1.) The spaces have the same load and schedule characteristics.
>
> 2.) Exterior zones with glazing must have the same, or similar
> orientation.
>
> 3.) Zones must be served by the same HVAC system or by the same kind
> of HVAC system.
>
>
>
> Chances are that the zones/spaces served by a single VAV box will meet
> these criteria in a properly designed HVAC system.
>
>
>
> Regards,
>
> Bill
>
>
>
> *William** Bishop, PE**, BEMP, LEED® AP **|** **Pathfinder Engineers &
> Architects LLP***
>
> Mechanical Engineer
>
>
>
> 134 South Fitzhugh Street Rochester, NY 14608
> T: (585) 325-6004 Ext. 114 F: (585) 325-6005
>
> wbishop at pathfinder-ea.com www.pathfinder-ea.com
>
> P Sustainability – the forest AND the trees. P
> ------------------------------
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Rob Hudson
> *Sent:* Friday, November 12, 2010 9:22 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Thermal Zones
>
>
>
> Hypothetically speaking, if i have a proposed design of a packaged VAV
> system where each VAV serves a range from 1 to 3 rooms, does my baseline
> design make the rooms serves by each VAV box a thermal zone or is each and
> every room its own thermal zone?
>
> So if i have 10 VAV boxes each serving 3 rooms, is it 10 thermal zones or
> 30 thermal zones?
>
> --
> Rob Hudson
>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101112/4659ecfd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101112/4659ecfd/attachment.jpeg>
More information about the Bldg-sim
mailing list